TwoBlocked
Senior Member
- Location
- Bradford County, PA
- Occupation
- Industrial Electrician
Pretty sure I got this right, but would like some verification.
A wall in a typical industrial site needs receptacles every so many feet with all raceways being rigid conduit. A horizontal conduit with tees is run up near the ceiling. At each tee a conduit is run to a few feet from the floor where they end in receptacle outlets. The conductors are daisy chained from one receptacle to the next with 4 current carrying conductors in the vertical conduits and 2 current carrying conductors in the horizontal conduits. Lets say 10 receptacles on a 20 amps breaker with #12 THHN wire.
Paragraph 2 of 310.15(A) states "The temperature and correction and adjustment factors shall be permitted to be applied to the ampacity for the temperature rating of the conductor, if the corrected and adjusted ampacity does not exceed the ampacity for the temperature rating of the termination in accordance with the provisions of 110.14(C)."
So we look at Table 310.15(C)(1) and get an adjustment factor of 80%. Applying this to #12 THHN , 90deg column of Table 310.16 we get 24 amps (30 x .80 = 24). This does not exceed the ampacity shown in the 75deg column (25A), Also it is greater than the maximum sized OCPD for #12 wire (20A) as per 240.4(D). I find the same thing with conductors #18 thru #10. They can be daisy chained without lowering the max ampacity of the OCPD.
Bottom line is you can run up to 6 current carrying THHN conductors #18-#10 in a raceway without downsizing the OCPD.
Right or wrong, or is there more?
A wall in a typical industrial site needs receptacles every so many feet with all raceways being rigid conduit. A horizontal conduit with tees is run up near the ceiling. At each tee a conduit is run to a few feet from the floor where they end in receptacle outlets. The conductors are daisy chained from one receptacle to the next with 4 current carrying conductors in the vertical conduits and 2 current carrying conductors in the horizontal conduits. Lets say 10 receptacles on a 20 amps breaker with #12 THHN wire.
Paragraph 2 of 310.15(A) states "The temperature and correction and adjustment factors shall be permitted to be applied to the ampacity for the temperature rating of the conductor, if the corrected and adjusted ampacity does not exceed the ampacity for the temperature rating of the termination in accordance with the provisions of 110.14(C)."
So we look at Table 310.15(C)(1) and get an adjustment factor of 80%. Applying this to #12 THHN , 90deg column of Table 310.16 we get 24 amps (30 x .80 = 24). This does not exceed the ampacity shown in the 75deg column (25A), Also it is greater than the maximum sized OCPD for #12 wire (20A) as per 240.4(D). I find the same thing with conductors #18 thru #10. They can be daisy chained without lowering the max ampacity of the OCPD.
Bottom line is you can run up to 6 current carrying THHN conductors #18-#10 in a raceway without downsizing the OCPD.
Right or wrong, or is there more?