I can?t quite figure out from the OP if the inspectors objection was in reference to 404.7 only or was about motor appliance disconnects, 422
If it was about 422, then to recap what others have said, (NEC2005 references)
422.30, we know that we need a disconnect.
422.31 (B) addresses permanently connected appliances over 1/8th hp. It says a switch or CB can be used if it is in sight and a provision exists for locking the switch or CB and that lock always remains in place.
422.32 says if you use a switch or CB as disconnecting means for permanently connected motor driven appliances over 1/8 hp, it should be in sight from motor controller, then contains an exception in the case of a motor driven appliance over 1/8 hp having a unit switch. As Iwire mentioned, disposals don?t have unit switches.
IF cord and plug connected, plug serves as disconnect.
If it was about 404.7, I can?t see how you could use a decora switch anywhere (which tells me that I am missing something).
If it was about 422, then to recap what others have said, (NEC2005 references)
422.30, we know that we need a disconnect.
422.31 (B) addresses permanently connected appliances over 1/8th hp. It says a switch or CB can be used if it is in sight and a provision exists for locking the switch or CB and that lock always remains in place.
422.32 says if you use a switch or CB as disconnecting means for permanently connected motor driven appliances over 1/8 hp, it should be in sight from motor controller, then contains an exception in the case of a motor driven appliance over 1/8 hp having a unit switch. As Iwire mentioned, disposals don?t have unit switches.
IF cord and plug connected, plug serves as disconnect.
If it was about 404.7, I can?t see how you could use a decora switch anywhere (which tells me that I am missing something).