Re: Dedicated Circuit for referigerator
Originally posted by pierre:
A duplex receptacle is not 1 receptacle, it is 2 receptacles. Since it is 2 receptacles, if you were to install a duplex receptacle, it would not be an individual branch circuit
Pierre in my opinion both you and the handbook are stretching things a bit.
I agree a duplex is not one receptacle.
A duplex is also not utilization equipment.
Branch Circuit, Individual. A branch circuit that supplies only one utilization equipment.
We can argue about intent till the cows come home however only what is written is actually code.
It appears to me that I could install 100 receptacles on a circuit and as long as only one piece of utilization equipment is plugged into at a time it would still be an individual branch circuit.
Think about a industrial environment where several welder receptacles are installed on one breaker. They roll the welder from place to place as needed. IMO this would still be an individual branch circuit.
Many issues in the NEC are similar.
We can feed a 200 amp disconnect with 125 amp conductors even though someone
may put larger than 125 amp fuses in it.
We can use a 40 circuit panel with only 6 breakers in it as the disconnecting means for separate structure even though someone
may later install more breakers.
I can not see how an inspector could force the use of a single receptacle.