OK... you have two standard radial circuits other than the lighting circuit in use in the UK... the first one uses a 20 amp breaker and 2.5 wire, and is used for up to 50 square meters of floor space...
Second is for up to 75 square meters of floor space and uses a 30 amp or 32 amp breaker and 4 mm wire.
the ring final is used for up to 100 square meters of floor space and uses 2.5 wire on a 30 or 32 amp breaker.
Technically unlimited outlets on each of them but spurs are only allowed one outlet unless the spur is a fused junction style of junction.. thus fusing the spur where it begins at.
Heating circuits for electric heating, loads of more than 2KW such as hobs and cookers, etc, are on their own dedicated radials, with appropriate sized breakers or fuses...
So, other than the radials and the way stuff is listed and regulated, not a whole lot of differences between USA and UK other than the way the devices are made... most of the rules concerning where outlets go are pretty similar to the ADA rules in the USA... or the IEBC rules and old IEC rules... from when there was an IEC and an NEC code book.