I've had this thread open and sitting for a while. Many may have posted by the time I've hit "submit", so if I'm disjointed from the conversation at this point, forgive me. I've been looking at the March 2006 UL Wire & Cable Marking Guide PDF, and still haven't found anything concrete for either side.
"Underground" is not a listing parameter mentioned in the table found on page 10 of the guide. "Direct Burial", "Outdoor", "Sunlight Resistance" are, but "Underground Use" is not.
I believe the intent is not to forbid a wet-rated cable for underground use, but this precarious premise Mike and MPD are hanging their hat on holds water.
From the guide:
One important note in my opinion, is that everythings talking about what the cables are "for", as in, initially designed to do. Nothing is prohibitive in any of the text I've reviewed. SE may have been designed for aboveground use, but there's not a word of prohibition to enforce that design, that I can see.
"Underground" is not a listing parameter mentioned in the table found on page 10 of the guide. "Direct Burial", "Outdoor", "Sunlight Resistance" are, but "Underground Use" is not.
I believe the intent is not to forbid a wet-rated cable for underground use, but this precarious premise Mike and MPD are hanging their hat on holds water.
From the guide:
Type SE ? Indicates cable for aboveground installation. Both the individual insulated conductors and the outer jacket or finish of Type SE are suitable for use where exposed to sun.
Types USE and USE-2 ? Indicates cable for underground installation including direct burial in the earth. Cable in sizes 4/0 AWG and smaller and having all conductors insulated is suitable for all of the underground uses for which Type UF cable is permitted by the NEC. Types USE and USE-2 are not suitable for use in premises or aboveground except to terminate at the service equipment or metering equipment. Both the insulation and the outer covering, when used, on single and multiconductor Types USE and USE-2, are suitable for use where exposed to sun.
One important note in my opinion, is that everythings talking about what the cables are "for", as in, initially designed to do. Nothing is prohibitive in any of the text I've reviewed. SE may have been designed for aboveground use, but there's not a word of prohibition to enforce that design, that I can see.