INGMRS
Member
- Location
- san jose, Costa Rica, code NEC USA
Hello,
I am confused with the calculation of the main disconnection of a photovoltaic inverter, in the inverter data sheet it is said that the maximum AC output current is 145A, then, as I understood, the way to calculate the OCPD is to multiply this current value by 125%, and the current would be 181.25A and the switch 200A.
But when I review the data sheet, the maximum external AC overcurrent protection is: 225A, how is that possible?
Could someone help me clarify this dobut,
Thank you!
I am confused with the calculation of the main disconnection of a photovoltaic inverter, in the inverter data sheet it is said that the maximum AC output current is 145A, then, as I understood, the way to calculate the OCPD is to multiply this current value by 125%, and the current would be 181.25A and the switch 200A.
But when I review the data sheet, the maximum external AC overcurrent protection is: 225A, how is that possible?
Could someone help me clarify this dobut,
Thank you!