kwired
Electron manager
- Location
- NE Nebraska
The following is a snapshot of the email response that I received from the inspector this morning.... is this where AHJ pulls rank?
Mr. Temple
300.5 Underground Installations
D ) Protection from Damage - is referring to all types of underground installations.
Trenching is the most common method used for installing electrical wiring so
“trench” is instructing the installer to include the warning ribbon.
D) 3) “Service” Conductors. The intent of this extends further than other types of underground installations because;
“warning ribbon reduces the risk of an accident, such as electrocution or an arc-flash incident, during excavation near underground service conductors that are not encased in concrete, because these circuits are not protected from short circuit or overload.”**
If directional boring can be done for the conductors then warning ribbon can be bored just above the Service Conductors.
The ultimate goal is to ensure the safety of the general public.
I’m still insisting on a warning ribbon if this Service is indeed moved underground.
Sincerely,
-------
Ask him what the words "direct-buried conductors and cables" that is written in (D) gets turned into "all underground installations".
If your locality wants it to mean "all" they really should have an official amendment to this section in their local ordinances somewhere and if so that is what he should be referencing rather than NEC content that doesn't say what he claims it says.