I don't do resd. 2 questions how many recp. can you put on 15 amp circuit i say doesn't matter. the guys say you can only go 80% of the breaker ampacity i laught at them hope i am wright
I would have laughed too. You are correct.
Just make sure that when you are talking about the 80% rule, that only applies to continuous loads. It's not an across the board rule that you can only load a breaker 80%.
just throwin it out there, aren't breakers only rated 80% though? you can buy 100% breakers but they're expensive. Never fully understood this
I'm not really sure where that idea came from but it sounds like a really good trade myth to me.
You can load an OCPD to its handle rating for 2 hours, and 59 seconds and then shut it off and you are fine. The 80% rating applies to continuous loads only.
I understand the continous load rule,but, but I think breakers are only rated at 80%.
I understand the continous load rule,but, but I think breakers are only rated at 80%. i'm hopin someone chimes in and shines some light on this for me.
call me crazy i always thought 20 amp brk was good up to 20 amp draw
thanks guys i know who is buying lunch tomm.
You're making this too complicated. It's really that simple...breakers are rated at their ampacity. The limitation on the ampacity is because of the continuous load rule.
providence thanks for the imput this is a great forum you guys really know your stuff
Ask how much of that 80% they assign to each receptacle. Then remind them that one 15a receptacle is 100% of a 15a circuit.I don't do resd. 2 questions how many recp. can you put on 15 amp circuit i say doesn't matter. the guys say you can only go 80% of the breaker ampacity i laught at them hope i am wright
. 21 amps may never trip it, 22 amps may take 4 hours, 23 amps may take an hour, 24 amps may take 10 minutes.... It's called a trip rating curve or something like that.