discusion at work
mistabass
Rhode Island
I don't do resd. 2 questions how many recp. can you put on 15 amp circuit i say doesn't matter. the guys say you can only go 80% of the breaker ampacity i laught at them hope i am wright
I would have laughed too. You are correct.
Just make sure that when you are talking about the 80% rule, that only applies to continuous loads. It's not an across the board rule that you can only load a breaker 80%.
just throwin it out there, aren't breakers only rated 80% though? you can buy 100% breakers but they're expensive. Never fully understood this
I'm not really sure where that idea came from but it sounds like a really good trade myth to me. :)
You can load an OCPD to its handle rating for 2 hours, and 59 seconds and then shut it off and you are fine. The 80% rating applies to continuous loads only.
I understand the continous load rule,but, but I think breakers are only rated at 80%. i'm hopin someone chimes in and shines some light on this for me.:confused:
Breakers are rated for 100% of the load. "Continuous load" derating only applies to conductors.
call me crazy i always thought 20 amp brk was good up to 20 amp draw
A 20a breaker can actually hold more than 20 amps. It will not magically trip at 20.0000001 amps, but the higher the amperage goes, the quicker it trips. 21 amps may never trip it, 22 amps may take 4 hours, 23 amps may take an hour, 24 amps may take 10 minutes.... It's called a trip rating curve or something like that.
thanks guys i know who is buying lunch tomm.
I'll be there! Where is it?
Print this picture out ....and ask them:
- How many circuits are needed?
:grin:
"Various types of low-voltage circuit breakers have differing continuous
duty capabilities. Some are rated to carry 100 percent of
their trip rating continuously while others are rated to carry only
80 percent of their trip rating continuously. It is important that we understand
the difference and apply these breakers properly"
Ask how much of that 80% they assign to each receptacle. Then remind them that one 15a receptacle is 100% of a 15a circuit. ;)
Before anyone starts claiming a free lunch at someone else's expense, let me say that I think the wrong answer has been given. I don't want this to become a side track or a rehash of old discussions. But I will say that I don't believe there is any limit to the number of receptacles you can put on a circuit. I will add that it does not matter whether you are talking residential or not.
I will conclude with a request (demand, actually ;)) that before either (1) you ask me to explain my reasoning, or (2) you try to tell me my answer is wrong, you first go find the other threads (there are several) in which this issue has been debated. Tell me you have read the other threads, before posting a comment in favor of, or in opposition to, my statement.
We now return you to your regularly scheduled discussion. :grin: