SameThe derating is the same as for any other conductors, but if it is only marked DLO, you can't use it for an NEC application. To be used in an NEC application it has to be marked with one of the wire types found in Table 310.104(A) or Table 310.13(A) in older codes.
You can find it with the required markings...usually is it DLO/RHH or something like that.
Note that you cannot normally use the ampacities listed by the manufacturer for an NEC application ...they typically list the free air 90°C ampacities.
The DLO does not come in the typical wire sizes....I normally use the Table 310.15(B)(16) ampacities for the next smaller size conductor. For example, for the 535.3kcmil DLO cable I use the 500kcmil ampacity from the table.
Can anyone tell me if it is true that more than single DLO cable in a conduit starts the derating process per 2011 NEC 310.15(B)(3)(a)?
At least they give you 75°C ampacities and both free air and conduit. Most only give you 90°C in free air.Look at the mfgs data
http://www.pittsburghwire.com/pdf/CatalogD24.pdf
Same
yup. i've done cable bus, and there was no derating,
but it was racked and ran not touching other stuff in the tray,
so maybe it's allowed to run with free air ampacity. there's
phenolic blocks, and it was in a 2' wide tray, 4 layers, 8 across, iirc.
i think it was 929 MCM or some odd size... a changeover at fox news,
started friday night before superbowl sunday.... we worked 30 hours
nonstop... what a perfect time to change out the transformer that
was going to power satellite feed for the superbowl, 'eh?
one more example of DWP = department of worthless planning.
It is not just the connectors on the wire, but it is also the rating of what the connectors are landed on. There are some applications where you can use the 90°C rating, but they are rare....
He tried the 75 degree C terminations angle until I showed him that the high press connectors I am using are listed at 90 degrees C and then came back with so much nonsense, it's driving me nuts. ...
At least they give you 75°C ampacities and both free air and conduit. Most only give you 90°C in free air.
Not sure if you can use the manufacturer's ampacities for the non-standard sizes. I would check with the AHJ before using those ampacities.
One of the problems I've seen with it is what was talked about here, the fact that not all DLO cable bears the right listings. Cable mfrs make straight DLO, no RHH listing, and it sells for less, especially when surplus houses get hold of it and word-of-mouth on a great price spreads. Contractors who don't realize the difference use it, then get tagged on a job. You just need to be careful, as always, when a deal looks too good to be true.
The other problem I see is the lugs issue. That's been getting better not only because of education through forums like this and word of mouth, but because there are more lug and terminal block mfrs addressing the issue by providing listed products. But again, careful attention to details is key.
Note that you cannot normally use the ampacities listed by the manufacturer for an NEC application ...they typically list the free air 90°C ampacities.
The issue is that there is no provision in the NEC that lets you make that adjustment and the increase in capacity is not a linear function of the cross sectional area. As long as your AHJ is fine, you are good to go.It may be prudent to seek pre-approval by the lahj but I personally don't see an issue as long as:
adjusted for actual cross sectional area per the NEC
insulation is certified to ICEA/UL/CSA specification
The jacket does have a lot of friction with the conduit if you are pulling it in conduit...make sure that you get 100% coverage of the wire pulling lube on the conductors so there are no high friction dry spots.a couple of caveats
insulation is not as abrasion resistant re: pulling in conduit
more expensive
I have used it for 1,500 hp DC motors for two reasons....there was very limited room in the DC drive to terminate the cables....they required a total of 16 cables, and more importantly the armature voltage was 750 volts. The DLO/RHH is available in 1,000 and 2,000 volt ratings, with the 2,000 being more common. My conduit runs were 150-250 long and it pulled with no issues.I usually see this stuff used in portable power centers where flexibility is required and large quantities are not required ...
The issue is that there is no provision in the NEC that lets you make that adjustment and the increase in capacity is not a linear function of the cross sectional area. As long as your AHJ is fine, you are good to go.
The jacket does have a lot of friction with the conduit if you are pulling it in conduit...make sure that you get 100% coverage of the wire pulling lube on the conductors so there are no high friction dry spots.
I have used it for 1,500 hp DC motors for two reasons....there was very limited room in the DC drive to terminate the cables....they required a total of 16 cables, and more importantly the armature voltage was 750 volts. The DLO/RHH is available in 1,000 and 2,000 volt ratings, with the 2,000 being more common. My conduit runs were 150-250 long and it pulled with no issues.
For most AHJs, that requires a stamped calculation from a registered PE....not a statement from a manufacturer.2011 310.15.(C) Engineering Supervision
that is how the manufacturer calculates the ampacity ....
I have used it for large DC motors because the termination spaces at both the motor and the drive were cramped and because the motors had a 750 volt armature. This was in conduits and the runs were 150-200'. The motors required four 4" conduits with each conduit having four 535.3 kcmil DLO/RHH/RHW conductors.Doesn't it defeat the purpose to put DLO cable in a raceway? I've used the stuff in free air to facilitate a flexible connection, but always with a splice box to connect to THWN-2 in raceway.