Absolutely not.Well, whats the answer? Do you have to use the grid for elevated tubs on decks. I was sure you did not have too? Yes or No?
Absolutely not.Well, whats the answer? Do you have to use the grid for elevated tubs on decks. I was sure you did not have too? Yes or No?
which brings us full circle :smile: the Code reference for "absolutely not" is ????Absolutely not.
I know Rob, but I didn't want to go into all that and deviate from the focus of this thread. I was merely pointing out that our DCA does make some exceptions to certain code sections.Actually NJ has a few exceptions in the 2008 NEC adoption.
which brings us full circle :smile: the Code reference for "absolutely not" is ????
Gus, Please send me a PM next time you do a spa tub on an elevated deck. I'd give a week's pay just to come down to Tenn. and watch you staple a bonding grid under a deckwhich brings us full circle :smile: the Code reference for "absolutely not" is ????
Getting back to the OP, if this spa tub is sitting directly on soil or grass with no specific walkway installed, a bonding grid is not required.
The perimeter surface shall extend for 1 m (3 ft) horizontally beyond the inside walls of the pool and shall include unpaved surfaces as well as poured concrete and other types of paving.
OK. I'll buy into this. If you had a job to install this spa tub are you telling me that you would either lay the grid on the ground or take a sod shovel, lift up a layer of sod, install the grid under it and re-lay the sod ? You can't be serious about this can youGrass sure sounds like an unpaved surface to me.
OK. I'll buy into this. If you had a job to install this spa tub are you telling me that you would either lay the grid on the ground or take a sod shovel, lift up a layer of sod, install the grid under it and re-lay the sod ? You can't be serious about this can you![]()
Believe me, I'm all for being code compliant but I think I'd have a hard sell telling a customer that I have to dig up her sod, go down at least 4-6" (680.26 (B)(2)(b)(5) to install an EPBG and re-lay her sod. That's probably the part where they would say - forget it, I'll put down pavers or pour concrete. Then we have a moot point:smile::
I don't see where a hot tub is required to have a bonding grid. Spa's and hot tubs shall comply with the provision of part I and part IV. The requirements for equipotential bonding are in part II.
I don't see where a hot tub is required to have a bonding grid. Spa's and hot tubs shall comply with the provision of part I and part IV. The requirements for equipotential bonding are in part II.
No it attaches to the motor of the tub and any other metal parts. Like a pool it keeps everything at the same potential.OK, I don't do a lot of pools, actually I don't do any. So you have to bury a #8, 18"-24" from the inside wall, 4"-6" deep, following the contour of the hot tub and that's it? doesn't attach to the hot tub?
No it attaches to the motor of the tub and any other metal parts. Like a pool it keeps everything at the same potential.