I thought I knew the answers here, and then read four pages and either missed or never saw what I thought was true, so I will tell what I thought and someone elese can tell me where I am wrong.
2011 NEC 250.24(A)(1) states "The grounding electrode conductor connection shall be made at any accessible point from the load end of the service drop or service lateral, to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means."
To me, that means that the OP's question regarding the GEC connection was a simple, "It is legal." Those who state that the inspection department in there area doesn't "allow" it are either not operating under the NEC, or there is a State or local ordinance altering this code section. It doesn't state, "unless the AHJ doesn't like it."
However, I do believe a Utility Company can refuse to let the GEC to land in their enclosure, but why does every meter can I have ever seen have a ground lug in it?
Second, and more of an issue for me. I live in Florida, I confirm that there are thousands of homes that have a meter on the outside and a main disconnecting means as the main breaker in a panel somewhere inside the house. I have often wondered if this is something that changed around the 1989's or has just always been what I consider violated.
230.70 (A)(1) ...readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors. I can't find it right now, but I know there is a place where the NEC states conductors are considered outside the building when they are under the slab. Someone else please help with the code reference, but by exclusion one could assume that conductors run in a crawl space could be interpreted as inside or outside. None the less conductors in an attic for example, are INSIDE the building.
As such, the Florida installation such as my house, where a meter is on the back wall, and the conductors run 20 feet or more through the attic and down in to the main disconnect panel, (GEC to the meter and 3 conductors from meter to panel BTW) is not per the above code. In Ocala, they have determined that back to back is OK, they will look the other way if it is a couple feet in on a side wall, but put an elbow, LOB or anything else in the run and the disconnecting means must be outside in new installations, or meter/service replacement. In Gainesville, they define "nearest the point of entrance" as less that 10 feet of conduit with no boxes. So, an AHJ can define nearest the point, but they shouldn't be able to decide someone can run service entrance conductors across a building to an interior panel without overcurrent protection.