First of all, if it seems as though I am directing my comments at you personally I apologize, that is not the case.
Roger
Before you go to 250.24 go back and read 250.4(A)(1)(2) and (3), this will explain what grounding does and what bonding all the components together does.True...kind of (250.24.D lumps them all together) but as I said, it's still a separate ground connected to the neutral, even though it may be higher impedance due to earth resistance.
And what do you call the load side Ungrounded and Grounded conductor connections?To us, that makes it a customer connection.
The best reason is that for dispersing high voltage surges and lightning strikes (see the aforementioned 250.4(A)(1)) it keeps everything at the first point of connection and outside the structure.I can't see any real reason to connect the GEC to the neutral bus in the sealed section anyway.
And we would be as well.Here, the POCO connects power based on a "Temporary Power" tag from the building department. That does not guarantee that all of the electrical is finished. Once we seal the enclosure, we're done.
That's no problem either, this is always part of inspections before the Inspection department releases it to the POCO for energizing.Any final inspections of the grounding and bonding by the town includes the GEC connection. We don't want the seals cut to inspect.
Who manufactures the meter enclosures are you talking about? All that we use (multiple manufactures) has the neutral bar factory attached to the enclosure with a line/load neutral lug and a lug for the GEC. IOW's it is bonded to the can when it leaves the factory, nothing else needs to be done as far as a MBJ.We have given several training classes for their inspectors on problems with GEC's connected to the can but not jumpered to the neutral bus, as required in 250.24.A.4, and have asked them during the final to make sure it's properly connected. We found MANY that were not.
As I stated at the beginning of this post, I don't mean to be aiming at you personally but I have yet to see a good argument from any POCO on this issue that makes any sense.We, as a POCO, are not Code enforcers. Our linemen are not well versed in grounding and bonding, and they do the new service connections, install the meter and seal the panels. Not sure I understand all of the negative comments.
This is a problem with older neighborhoods that are still served by all metal plumbing and in this case it can actually be better to not have any connection to the GES. With no MBJ the lights and appliances will probably go haywire and give a heads up that there was a problem.Regarding the fatalities, we had a contract plumber get in series with the metal water pipe at a residence while installing a water meter. He was killed when he got across the open junction (voltage was measured at 120V). Investigation showed no MBJ connection, a loose neutral at the customer side bus and a loose GEC connection which arced when disturbed. It was decided that the neutral current was returning to the transformer neutral via the utility pole ground through the water pipe, not the neutral service conductor.
I understand that this is pretty much SOP everywhere now.We now require them to jumper across the junction before breaking the piping open.
And I think that is the way it should be but, the lowly GEC connection being made in a meter enclosure that is manufactured to accommodate it certainly isn't a hazard.Now we and the town are very careful about proper wiring. Sad story, but not the only one I've been involved in. Guess we choose to err on the side of caution.
Roger