- Lockport, IL
- Retired Electrical Engineer
I recently had a disagreement with an AHJ in California. We ultimately found a mutually acceptable solution. But I would like opinions on the original issue.
We are doing the electrical design for a restaurant. The designer of the kitchen equipment selected a table that had many different cooking capabilities. We were to supply a single set of conductors to a single point of connection. The table had a built-in enclosure with circuit breakers that served various points on the table. The table was UL listed.
The Inspector?s point of view was that,
Our point of view was that,
Any comments?
- The internal components of the table fell within the scope of the NEC.
- The wires from our circuit breaker to the table comprised a feeder.
- The enclosure with the breakers comprised a panelboard as described in NEC article 408.
- The wires from that panelboard to each individual point on the table were branch circuits.
- The panel schedule that was provided by the table?s manufacturer was not acceptable as evidence of a calculation of the load that is to be served by the panelboard.
- The panel schedule and load calculation for this panelboard was therefore required to be issued with the project?s plans and specs, and was required to be signed and sealed by the project?s Designer of Record (i.e., us).
- We were supplying branch circuit conductors to a UL listed appliance.
- The internal components of that appliance fell outside the scope of the NEC.
- No documentation of any wiring or load values associated with the appliance was required to be included in the project?s design documents.
Any comments?