Does volt amps = watts?
I have a queastion maybe you could answer for me. The guys at work are all wondering if it would be cheaper to run a single phase 110v motor load or any load for that manner oposed to single phase 220v, & why??
Thanks,
Brian
No:
No:
Thanks,
Brian
With 240V, the current would be cur in half and the copper losses would be reduced to one quarter relative to 120V--assuming the same wire size. The motor efficiency would likely be the same for a 120/240V motor.
Brian, for a given power, the higher voltage allows for less current, which is usually better: insulation is cheaper than conductor, and less heat is generated (or has to be sized to avoid).
rattus said:
weressl said:
rattus said:
Laszlo,
PF may be ignored with a resistive load, but it still exists. You cannot say a resistive load has no PF!
Laszlo, let me refresh your memory:
"No. A heater would have no power factor as it is purely resistive load. Inductive loads such as transformers and induction motors have power factors. Synchronous motors have no power factors either, so they are used sometimes to correct power factors in the plants."
I responded in so many words that a resistive load carries a PF of one although I understood what you meant. That is what started this little exchange.
..and let me refresh yours:
http://forums.mikeholt.com/showthread.php?p=782973#poststop
...where the yes and no answer was posted. Yes it has a value of 1 and no it does not have an effect on the result, in this case W=V*A, as pf=1 and 1 does not have meaning in a multiplication.
No sane person could argue that, but not altering the outcome doen't stop it from being a factor, mathematically speaking.
(I won't even say it has "no meaning", but I will agree it doesn't change the outcome.)
Would you also say that zero is not a factor in multiplication?
Mike03a3 said:
By now I assume you've read the paper attached to post #81, which confirms my statement.
That paper comes from the "little electrons" side. In power engineering that laid the foundation of the science of electrical engineering the term is clearly reflects on the relationship between U and I.
Stop playin' Humpty Dumpty; "words mean exactly what I want them to mean":D
Gentlemen, I was just wondering, did poor ole 220/221 get his question answered? Or did it get lost somewhere between 0 and 1 like I did?