downrod splices.

Status
Not open for further replies.

charty

Member
I was in Home Depot today and was surprised to see a wire extension kit for ceiling fans. It contained some wire and butt splice crimps. I haven't looked this up in the NEC yet but I would think that splicing conductors in downrods would be a violation, if not poor workmanship. It stated on the package " To be installed by a qualified electrician". Am I wrong here?
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: downrod splices.

You decide!

2002 NEC
300.13(A) General. Conductors in raceways shall be continuous between outlets, boxes, devices, and so forth. There shall be no splice or tap within a raceway unless permitted by 300.15;............

310.15(A) Wiring Methods with Interior Access. A box or conduit body shall not be required for each splice, junction, switch, pull, termination, or outlet points in wiring methods with removable covers, such as wireways, multioutlet assemblies, auxiliary gutters, and surface raceways. The covers shall be accessible after installation.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: downrod splices.

I would say this may be a UL listed accessory kit to a UL listed fan.

As such the NEC would not apply.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: downrod splices.

Think of a typical dishwasher.

Do you fail the installation of it because of the factory exposed live connections and open conductors enclosed by the floor, cabinet sides and wall?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: downrod splices.

Common sense, (heard he died) and if safe in reality, no problem.

We have way to much in listings, codes, standards, red tape thumpers etc...

Roger
 

charty

Member
Re: downrod splices.

i would say that if an electrician was in court for an electrical fire with fatalities and was asked "Why didn't you follow NEC requirements?" Then he is in trouble. I don't think that UL would be on the stand.
So I would say that UL has more power, but you better comply with the NEC.It's all about how you use those UL listed products.
 

ryan_618

Senior Member
Re: downrod splices.

:D Now I didn't say one way or the other if I would red-tag a fan install because of the splice. The truth of the matter is I would never know.

Bob: I've never really looked at the underside of a dishwasher. When I installed mine, there was a nice little enclosed box for the termination of the branch circuit conductors. If the appliance is wired from the factory in a non-compliant manner, it is beyond the scope of the NEC
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: downrod splices.

Originally posted by ryan_618:
Bob: I've never really looked at the underside of a dishwasher. When I installed mine, there was a nice little enclosed box for the termination of the branch circuit conductors. If the appliance is wired from the factory in a non-compliant manner, it is beyond the scope of the NEC
Hey I know you where just asking. :)

Yep they have a nice enclosed box for the field wiring to terminate in.

From there it leaves the box and goes single conductor in free air.

You will also find solenoids and such with exposed terminals.

Now if we agree this is beyond the scope of the NEC why would parts form the factory with instructions on how to install them be any different?

Of course I like Rogers answer best. :) :cool:

Common sense, (heard he died) and if safe in reality, no problem.
In the application we are talking about what would be the problem?
 

hurk27

Senior Member
Re: downrod splices.

If we are allow to have a splice in surface raceway then what would be the problem?

310.15(A) Wiring Methods with Interior Access. A box or conduit body shall not be required for each splice , junction, switch, pull, termination, or outlet points in wiring methods with removable covers, such as wireways, multioutlet assemblies, auxiliary gutters, and surface raceways . The covers shall be accessible after installation.
 

stamcon

Senior Member
Re: downrod splices.

Once the wires leave the ceiling box(hopefully there is one), aren't the wires now part of the fixture and not under NEC rules for splices? I would think the downrod is part of the fixture and not a surface raceway, etc. Personally I would pull new conductors and not splice in the rod.

steve

[ December 11, 2003, 09:47 PM: Message edited by: stamcon ]
 

ryan_618

Senior Member
Re: downrod splices.

I'm wondering if the extension wires with the butt splices are intended to be spliced inside of the downrod, or in the motor housing? I would think inside of the motor housing. When you assemble a fan, you have to run the conductors through the downrod, whether it's 10 feet or 4 inches. I think you have plenty of room to splice without doing it illegally.

Is anyone going to die over it? No.
Can a code compliant installtion be done easily? Yes.

I also like Roger's answer though. ;)
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: downrod splices.

Originally posted by hurk27:
If we are allow to have a splice in surface raceway then what would be the problem?
IMO that is a different issue.

A surface raceway you may want to add to / fish etc.

There is nothing you could or would want to do in this down rod without dropping the fan.

I know I would do it with out a second thought. :)
 

bill addiss

Senior Member
Re: downrod splices.

Personally, I would consider the Downrod as being part of the Fixture. There are already splices in many Fixtures that are only accessible after dismantling it.

Bill
 

pierre

Senior Member
Re: downrod splices.

Bob
The dishwasher open wiring that you speak of is not installed by the electrician. The wiring for the down rod most certainly is not wired by the manufacturer, therefore I say the NEC has plenty to say about it. Ryan's last post is quite accurate in that the conductors should be spliced not in the rod, but the canopy of the fan.

Pierre
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: downrod splices.

I do not agree with you Pierre if this is a UL listed kit provided by the manufacturer and the instructions say splice in the rod then the NEC is not involved.

Say you buy an ice maker kit to add to your freezer, do think the wiring you are doing would be under the NEC?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: downrod splices.

I agree with Bob. If the NEC recognizes UL for some situations, they have to recognize all UL listings.

In other words, selectivity is not an option.

Roger
 