210.23 states "In no case shall the load exceed the branch circuit amperage rating".
and it won't because the breaker will trip.
210.23 states "In no case shall the load exceed the branch circuit amperage rating".
I'd say that, reading Art. 210.21, Table 210.21(B)(2), and Art. 210.23(B), it is permissable.hillbilly said:I disagree.
210.23 states "In no case shall the load exceed the branch circuit amperage rating".
If I'm using one 30A circuit to feed (2) 5000 watt clothes dryers, then ...IMO... I've violated this rule.
I don't read anything in 210.23 that would allow this.
haskindm said:Have you done a service load calculation to determine if the service is adequate for the load of the additional dryer? If it is, then set a small sub-panel to provide the needed circuit. The cost would be minimal. If they can afford two dryers, and the electricity to run them, they can afford a sub-panel in order to do the job right. If they refuse, then run, do not walk, to the nearest exit and let someone else fool with this mess.
petersonra said:and it won't because the breaker will trip.![]()
LarryFine said:I'd say that, reading Art. 210.21, Table 210.21(B)(2), and Art. 210.23(B), it is permissable.
I agree with you that this is the crux of the issue. :smile:hillbilly said:I guess that this is where we agree to disagree.
The cause of confusion (in my mind) is the difference between fixed loads verses receptacle outlets.
Again, does the presence of receptacles make a difference? Let's play:Is the concensus here that it's allowed to add as many fixed loads as I want to a 30A circuit, as long as the largest of the loads doesn't exceed 80% of the circuit ampacity?
Can I add 3, 4, 5...etc... 24 amp (max) fixed loads to a single 30A branch circuit?
LarryFine said:most people only use one dryer at a time.
wirebender said:I don't even know anyone that has more than one dryer, unless you count the ones in the junk pile on the back lot.![]()
iwire said:But now when the circuit size changes to 30 amps everyone is getting all worried......I don't understand it at all.
Actually I use the clotheline in our backyard for about half of the year. So you might say I use 1/2 a dryer! Still a 30 amp circuit thoughwirebender said:I don't even know anyone that has more than one dryer, unless you count the ones in the junk pile on the back lot.![]()
Okay, there's that "fixed in place" term again. I don't see it defined in Art 100, so what is it? "Fixed" sounds like "hard-wired" to me. Are dryers "fixed" or merely stationary?georgestolz said:If we connect two fixed-in-place dryers to the same circuit totalling over 30A, how are we complying with this rule? Sure, 210.23(B) says that any one load can't exceed 80% of the circuit, but how does that negate the primary requirement that we not overload any circuit?
"Fixed" sounds like "hard-wired" to me.
Dennis Alwon said:If I had 3 - 15 amp motors to wire at a factory. Each was 120 volts. I decided to hard wire them. You are then saying I would have to have 3 circuits run to these motors. Now I decide to use a cord and plug. I can use one circuit to wire all 3 motors??????
Doesn't sound right to me.
iwire said:I can't believe this is still going. :grin:
Everyone of us has put more then one 20 amp duplex on a 20 amp circuit.
Many times there will be more load plugged into the circuit then the circuit could handle at once. Say the SABC, with a toaster, coffee maker, can opener and radio all plugged into it....that would likely be over 20 amps.
It happens all the time.
But now when the circuit size changes to 30 amps everyone is getting all worried......I don't understand it at all.