Let me help. Though Eaton says it is, it doesn't mean it actually is!
As 240.86 provides, you are given 2 options and a prohibition:
One, it is a selection of a fuse/ breaker combination done by a licensed PE, the documentation available for others to those authorized to design, install, inspect, maintain, and operate the system; the PE ensures that the downstream protective device remains passive during the interruption (by the upstream protective device); signs, and seals/ stamps the correctness of the selection, etc.
Two, and the easier way, is to get tested series-rated combinations from manufacturers of these protective devices.
Prohibition is to never use a series-rated combination if motor circuits are connected between the higher-rated overcurrent device and the lower-rated device and the motor full-load currents exceed 1% of the interrupting rating of the lower-rated protective device.