A current limiting reactor is impedance which is recognized in 110.10 as one thing to be considered when determine the available fault current.
The NEC does not describe how available Short Circuit Current should be calculated. It does say Listing requirements for industrial control panels, elevator controls, and HVAC control panels need to be followed. There is no fuse manufacturer with a published short circuit analysis procedure, like Eaton's point to point method, that includes their fuse performance.
UL has special 'umbrella' fuses which it uses in its listing process partly to accommodate the fact fuses types and brands may be changed in the field.
Ok so what is this for? It's from cooper Bussmann:
How to Use the Let-Through Charts
Using the example given, one can determine the pertinent let-through data for
the KRP-C-800SP amp Low-Peak fuse. The Let-Through Chart pertaining to
the 800A Low-Peak fuse is illustrated.
A. Determine the PEAK let-through CURRENT.
Step 1. Enter the chart on the Prospective Short-Circuit current scale
at 86,000 amps and proceed vertically until the 800A fuse
curve is intersected.
Step 2. Follow horizontally until the Instantaneous Peak Let-Through
Current scale is intersected.
Step 3. Read the PEAK let-through CURRENT as 49,000A. (If a fuse
had not been used, the peak current would have been
198,000A.)
B. Determine the APPARENT PROSPECTIVE RMS
SYMMETRICAL let-through CURRENT.
Step 1. Enter the chart on the Prospective Short-Circuit current scale
at 86,000A and proceed vertically until the 800A fuse curve is
intersected.
Step 2. Follow horizontally until line A-B is intersected.
Step 3. Proceed vertically down to the Prospective Short-Circuit
Current.
Step 4. Read the APPARENT PROSPECTIVE RMS SYMMETRICAL
let-through CURRENT as 21,000A. (The RMS
SYMMETRICAL let-through CURRENT would be 86,000A if
there were no fuse in the circuit.)