Just how would you properly select the current limiting fuse? And just who would have to accept it to make it an acceptable solution?My point is 240.86 does NOT require a tested combination for SCCR of a downstream device. That section is for two OCOD's in series.
As it is, I see no NEC prohibition against using a properly selected CL fuse (no PE required) to reduce the fault current for SCCR purposes. I actually don't have a dog in the fight - If this isn't an "accepted" method, then the NEC needs to tell me it's not.
Conceivably, you might be able to use current limiting fuses in combination with some kind of circuit breaker for instance in series if you put it in a UL508a panel and used it as your feeder source.
Based on the charts and UL508A though that describe how you can do this it's not going to help you for much more than 30 or 60 amp circuits.