The new listing requirements have been changed to match the code rules and 230.85 require that the emergency disconnect "be marked suitable for use as service equipment, but not marked as suitable only for use as service equipment". The current listing standards will not permit that meter assembly be marked as required by the code rule.
UL 869A 14.1.1 is the only thing I see addressing the "
only" and that's just if the neutral is factory bonded to the can.
I don't see any enforceable safety issue with a "suitable
only for use as service equipment" disconnect having a neutral factory bonded to the can vs a "emergency disconnect" with a removable neutral bond. I don't see anything else about AFC or otherwise in the standard that differentiates the two disconnects.
On the contrary I think it would be much
safer if the emergency disconnect
had a factory bonded neutral that could not be inadvertently be removed.
If the alternative is the EC employs six two pole breaker enclosures tapped off a 3R gutter and call all six emergency disconnects I rather the EC use that Siemens meter.
Here is another example of a more typical install:
Say we have a 320A meter on a detached garage and one 200A disconnect for the garage & well pump and one 200A breaker for a feeder the house.
The conductors to the house would then be a feeder.
Now omit the 200A breaker and just continue the 3-wire conductors to the house, then they would be service conductors, still legal.
Now do you agree if we add back the 2nd 200A disconnects at the garage as an 'emergency disconnect' for the house the EC could still run a 3-wire feeder to the house? And it does enhance safety because now if there is a problem at the house the fire dept can kill the house breaker on the garage without pulling the meter and killing the water.