bobby ocampo said:
...At t=0 in transient principle if EGC is not bonded then there will be a potential to ground in the energized metal enclosure.
If you are still talking about an ungrounded system it must have ground fault detection without this it will be in violation of 250.21. Ungrounded systems are not code compliant to allow a short to remain and especially to be undetected. Again an ungrounded system without ground fault detection
completely circumvents the only reason for an ungrounded system!
If you are talking about a grounded system run a scenario: how long will your circuit stay energized with say .25 ohms on your effective ground fault path and a case frame short (any spec will do with ohms law)?
bobby ocampo said:
?If connection to earth will limit the potential to ground in High Resistance Grounded and UNGROUNDED SYSTEM
Exactly how will this happen at what distances? You will get great logical NEC guidance on this forum but now you're into the physics.
bobby ocampo said:
, why will it not reduce the voltage to ground in a SOLIDLY GROUNDED SYSTEM.
Because if you installed a code compliant circuit, or feeder, the OCP has opened in seconds or even milliseconds, the circuit will be off.
bobby ocampo said:
The coil of the transformer is not automatically de-energized at the instant of the single line to ground fault if it is not connected to earth...
On a grounded system it most certainly should be if you have installed an effective ground fault path!
Fault current is only trying to return to source, one short on an ungrounded system has no potential it?s like a bird on a wire. The earth grounding is still required and there will be zero use of electricity with a short. There is no potential to earth because none of the transformers are bonded.
Fault current is not trying to go to earth if it is the circuit is in violation of NEC.
If a fault happens I=E/R proves the need for an intentional equipment ground fault path to enable the operation of overcurrent protection.