bobby 0 -
bobby ocampo said:
IEEE Std 142-1991
"2.1.2 Electric-Shock Exposure
Electric shock injuries result from contact with metallic components that are unintentionally energized [10].7 Effective equipment grounding practices can minimize these personal injuries.
A breakdown of insulation can cause accidental contact between an energized electrical conductor and the metal frame that encloses it. Such contact tends to energize the frame to the voltage level of the conductor. Avoiding shock-hazard voltage requires nullifying this tendency. The equipment-grounding system should do this by forming a low impedance path to ground."
The current version of ieee142 is 2007. It doesn't read the same as your 1991 version. Perhaps the IEEE has learned a few things in the last 16 years.
Suggest you read the current version of 142, 2.1.2, particularly b and c. For impedance grounded or ungrounded systems, the IEEE is far more concerned with an effective path for fault current than attaching the metal parts to a conductor that has a low impedance to earth.
Also suggest reading the current version of 142.1.3 Purposes of system grounding.
Thirty years ago I completely understood NEC 250.4. Then about 20 years ago some of us started wondering just how the NEC came up with the physics that explained the reasoning behind 250.4. - there does not appear to be any. Oh yeah, lightning strilkes are easier to mitigate if the non-current metal parts have a connection to ground - but a 1000ohms is as good as the NEC mandated 25ohms.
Finally, the IEEE and the NEC are coming around. The term "bonding" is being differentiated from "grounding". Most of the issues you have been discussing are dealt with through bonding - As has been said, grounding adds very little to the safety.
You like thought experiments - this one has already been brought up, (iwire) but I'll change it a little and see if it makes sense to you:
Put an insulated (dry wood is fine) pallet out in the middle of your yard. set a metal structure on it (a bread box will work). Attach a single wire to a standard house service, grounded, 120/240V, 1pole, 20A cb - other end to the bread box. Wet the soil around the pallet. Turn on the CB. Measure the voltage to ground by sticking one probe in the wet earth at least 3 feet from the box, and the other probe on the box.
Voltage to ground = ???
Turn off the CB. Drive a ground rod and connect to breadbox. For this experiment, let's say the ground rod measures 25ohms to earth. Turn On the CB. Measure the current going to the bread box. Measure the voltage to ground. Make sure the earth probe is at least 3' from the ground rod.
Current = ???
Vbg = ???
What do you think will happen if you stand three feet from the ground rod and reach out an touch it?
Grounding the system did nothing to make it safe from a fault to the non-current carrying parts.
A direct fault to ground did not even draw enough current to trip a 20A Cb.
Square D's parent has some interesting papers on the subject. I think they are on Mikes Holt's site somewhere. Perhaps one of the posters know where they are. I think we Americans could learn a lot for the Norwegians (arrggg - Americans are not the best