Hello
I think the residential Electrical system needs to be earthed or solidly grounded to the earth with a grounding Electrode to earth.
Because, lets say we go with a system which has a floating grounding conductor system which is not earthed.All metal equipment and
construction materials are grounded to the grounding system which is floating or insulated from the earth.This has to be required to clear
faults to trip the breakers.
We are required by code to have outlets outside at front and back for outside work. We know the GFI probably want work since
the system is not earth.
Example of why and this is just one reason.
We have an extension cord plugged in for a hedge clipper and this clipper receptacle is on line #1.
If this extension cord had a nick of exposed wire on the hot side of the line #1 and was touching the wet ground
nothing would happen you would never know that the ground around you was energized, until you touched your in this case
aluminum siding on your house and received a fatal shock.
There are other reasons but this is the most simple to understand.
The worst thing I think about earthing a system is that the grounded high tension line has a direct connection to your neutral
that feeds your house.
I agree with Don that we do need this jumper for clearing high voltage faults where a high tension line falls onto one of your 240 volt
residential electrical system.