bobby ocampo said:I will conduct an experiment on a solidly grounded system but at a reduced voltage of 21voltsY/12 volts. I have already verified importance of connection to ground of the BONDED EGC in UNGROUNDED AND HRG SYSTEM.
Based on science and vector equivalent of electrical system, importance of connection to earth is very important. T
The ground connection is extremely important!
On a grounded system you will not have current (dangerous touch voltage) on the equipment grounding unless the circuit is in violation of NEC. The bonding of equipment to the transformer ensures this, a short will cause the circuit will trip or open, it will be off it?s a direct path from and to the transformer!
On an ungrounded system you will have ?ground detection? (indication/annunciation), if you don?t your circuit is in violation of NEC! According to Mike Holts ?Grounding versus Bonding? and ANSI/IEEE 142, ?One of the dangers of an ungrounded system is that system overvoltages can occur during arcing, resonant of near-resonant ground faults [1.4.2]. ?And, ?Field experience and theoretical studies have shown that arcing, restriking, or vibrating ground faults on ungrounded systems can, under certain conditions, produce surge voltages as high as six times normal.?
Again the above happens when an ungrounded circuit is misused and or in violation.