BarklieEstes
- Richmond, VA
- Master Electrician
Greetings,
I've heard "you can never put #8 romex on a 50a breaker", but my reading of the 2017 NEC suggests that it can be allowed. What am I missing?
The situation is a 40a EV Charger with #8 romex hooked to a 50a breaker.
334.80 says "The allowable ampacity shall not exceed that of a 60°C (140°F) rated conductor" (40a). I don't need the cable to allow more than 40amps though since it's a 40a charger. Nor does it seem like the words "allowable ampacity" refer only to non-continuous loads since the definition of Ampacity says "The maximum current, in amperes, that a conductor can carry continuously...". I am asking a #8 NM Cable to continuously carry 40a and 334.80 says that I am allowed to ask that of it.
210.19(A)(1)(b) says "the minimum branch-circuit conductor size shall have an allowable ampacity not less than...125 percent of the continuous load" (40 * 1.25 = 50a). The allowable ampacity of a #8 sized copper conductor is 50a when terminating to 75° lugs [Table 310.15(B)(16)]. The calculated current of 50a is not greater than the 50a ampacity of #8 copper.
Only if I read the words "allowable ampacity" in 334.80 to mean the calculated ampacity from 210.19 would this application be disallowed. Nowhere in the Code does it say to intermingle the calculated current vs conductor size ampacity test from 210.19 with the actual current vs reduced-rating ampacity test from 334.80. The Code reads these as two separate tests and this application passes both.
210.20(A) says that OCPD needs to be no less than 125% of my continuous loads (40 * 1.25 = 50a). Therefore, I have selected a 50a breaker.
I know I can't put a 50a non-continuous load like a stove on #8 romex, but it seems like I can put a 40a continuous load like an EV charger on it.
Regards,
Barklie Estes
Regards,
Barklie Estes