I spent a decent amount of time re-reading through yesterday and I am still unconvinced that 220.40 doesn't apply to parts 3, 4, and 5. It would be weird to just mention those sections in 220.40 and have them not apply just because it was found at the start of part 3.
Regardless, neither 220.82 or 220.83 include it and they state 'that the demand factors shall apply to the following' but only include loads found in chapter 4. Even 220.3's table doesn't include chapters 6,7,8. And it is phrased like only chapter 4 amends 220. As in installing solar wouldn't amend the service conductor calculation. Which I believe we all agree does. (The service conductors shouldn't be less than the solar).
I personally think it deserves the generator treatment where one section is in 400s and the other is encompassed by 700s when interconnection (Back feed) is considered.
I agree that 220 is antiquated. It is based on the old idea of someone can't use every receptacle, light, AC unit, heater, stove, etc. at the exact same time. Which is very true. I just don't think that applies to a EV charger that (without considering continuous factors) will be 48A on a board that if 100% rated is 200A. ~1/4 of the board by itself. Now, do I think that family is pulling close to over 120A without it? No. But I do not think applying a demand factor to the charger does the process justice.
This language doesn't exist in Part IV.
It does. 220.12 (part 2) is mentioned in 220.83(1)(A)
I think it all comes down to interpretation which sucks. "Load calculations shall include the following:" is both limiting you to the prescribed loads of A,B,C,D and excluding EV chargers from it's use. So someone can interpret it to exclude all other loads from the calculation. Or that the demand factors don't apply to EV chargers. But I don't see trying to put the EV charger into an appliance mold. It isn't one.