By applying the EVSE charger with a demand factor of 40% then you will end up overloading the service in no time. Lets say our magic number is enough VA to load up to 199A, so 47,760VA.
Lets start with Example D2(b) - we will add one 48*240=11,520
So the new total general load is 44,320.
10,000+(.4*34,320) (and then the AC from the example) so 23,728+10,080 = 33,808VA
We are less and if we do it the way I was suggesting, 29200VA (from example)+(11520*1.25) = 43600VA. Still good.
Lets add two chargers, new general load is 55,840VA, --> 38,416VA. I would say we are at risk of overloading the service, but lets continue until the optional method agrees.
3 chargers --> 43,024
4 chargers --> 47,632 (198.5A)
So 4 chargers is probably the most we are going to get.
4 chargers at full load, running continuously, at the same time, is a full load current of 192A and if you factor in the continuous load, you will be over 200.
Based on the optional method you are okay with 4 chargers and 310.12' reduction to have the lights, chargers, AC units, etc. running and be okay.
Based on good judgement, you are setting them up to trip their breaker or worse.
Lets start with Example D2(b) - we will add one 48*240=11,520
So the new total general load is 44,320.
10,000+(.4*34,320) (and then the AC from the example) so 23,728+10,080 = 33,808VA
We are less and if we do it the way I was suggesting, 29200VA (from example)+(11520*1.25) = 43600VA. Still good.
Lets add two chargers, new general load is 55,840VA, --> 38,416VA. I would say we are at risk of overloading the service, but lets continue until the optional method agrees.
3 chargers --> 43,024
4 chargers --> 47,632 (198.5A)
So 4 chargers is probably the most we are going to get.
4 chargers at full load, running continuously, at the same time, is a full load current of 192A and if you factor in the continuous load, you will be over 200.
Based on the optional method you are okay with 4 chargers and 310.12' reduction to have the lights, chargers, AC units, etc. running and be okay.
Based on good judgement, you are setting them up to trip their breaker or worse.