I definitely wouldn't use that with stranded wireThe cheap Levitons have screws that directly contact the wire.
I definitely wouldn't use that with stranded wireThe cheap Levitons have screws that directly contact the wire.
I definitely wouldn't use that with stranded wire
Wish. Got one AHJ demanding a stamped engineer print of entire structure wiring of an existing structure to put in an EV charger. Can't find an engineer doing electrical engineering for residential. Kind of explains some of the work quality I'm seeing in that area, no permits = no inspection = handyman specials.Most of the AHJ's in my area offer an expedited EV permit.
An EV charger can actually be challenging to inspect: high loads, sharing older panels, and don't get me started on EVSE equipment that can be set in software to a lower maximum amperage -- that just makes me shudder in terms of safety and inspection.
Is this just being required for EV charging, or any larger circuit? How is it that different than an electric range circuit?Wish. Got one AHJ demanding a stamped engineer print of entire structure wiring of an existing structure to put in an EV charger. Can't find an engineer doing electrical engineering for residential. Kind of explains some of the work quality I'm seeing in that area, no permits = no inspection = handyman specials.
Checked with one company that does do electrical prints (only large commercial projects) they might be willing to look at it if I draw it, for about $2000 - $3000. Big bump for a generally $500 - $1000 + materials job.
I see them as 100% exactly the same kind of a install as a large hot tub. Similar install methods and load size.Is this just being required for EV charging, or any larger circuit? How is it that different than an electric range circuit?
They may be the same in new construction, but in retrofit it's different because nobody planned enough capacity for a SECOND electric range in the panel. I work in an area with 50-100 year old electric panels mostly.I see them as 100% exactly the same kind of a install as a large hot tub. Similar install methods and load size.
I'd still use a wiring method that'd allow 50 amps after a service upgradeThey may be the same in new construction, but in retrofit it's different because nobody planned enough capacity for a SECOND electric range in the panel. I work in an area with 50-100 year old electric panels mostly.
That said a 240V 20 or 30 amp is actually really quite OK for most people. 50A for EVs is pretty standard, but all night at 240V 20 amp even does most people pretty darn good.
Word. Yes.I'd still use a wiring method that'd allow 50 amps after a service upgrade
No, it's not that so much.What I heard was some EV drivers carry their EVSE with them when they travel and if necessary they will locate an RV park with NEMA14-50R, I guess the charging station build out is not yet quite enough everywhere.
Not sure, This AHJ (not electrical inspector) demand as worded would imply it doesn't matter what is being installed or upgraded. Demands "Stamped Prints". I have no problem providing load calcs, upgrade specifications, etc., but there doesn't exist an engineer doing any level of "residential" electrical prints nor is it required in state codes for residential 1-2 fam.Is this just being required for EV charging, or any larger circuit? How is it that different than an electric range circuit?
Submit your permit application and get a rejection in writing from him.Locally it has been suggested by several that this AHJ has a personal agenda to block EV from any of his jurisdictions.