Extension cord

Merry Christmas
Status
Not open for further replies.

the blur

Senior Member
Location
cyberspace
A garage door opener operates for 30 seconds. I see no problem using a 16 ga SJ cord. Even the lamps are LED's, so that, and a direct drive motor has no startup current. I'd even do 18ga lamp cord across the ceiling.
 

BillyMac59

Senior Member
Location
Wasaga Beach, Ontario
Occupation
Industrial Electrician
Will it work? Yes. Is it code compliant? Of course not. As "hbiss' stated, it cannot be stapled. Once secured in place, it would be interpreted as a permanent wiring method. Flexible cable doesn't fall in that category.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Will it work? Yes. Is it code compliant? Of course not. As "hbiss' stated, it cannot be stapled. Once secured in place, it would be interpreted as a permanent wiring method. Flexible cable doesn't fall in that category.
What if he hung the extension cord from cup hooks screwed into the ceiling? It would then not be secured.
 

garbo

Senior Member
Can i run a extension cord stapled to celling of my garage for a garage door opener ??????????????????????????????????????????????????????????????????????????????????
No. Was always told that an extension cord can never be used in place of a permanent wiring method. Besides over time rubber on cords deteriate and crack. I would install EMT conduit or metal wire mold. Do not like using plastic wire mold near work benches or garages where it could get damaged. Had a customer call me to run a new receptacle 3' from existing receptacle due to fire Marshall writing them up for using a 3' extension cord to feed a wall clock. The extension cord that I removed was over 20 years old and same type that is on a residential table lamp. ( does anyone still call it zip code ? ) It was dry rotted cracked and even while only providing a few watts to clock a fire Hazzard.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Had a customer call me to run a new receptacle 3' from existing receptacle due to fire Marshall writing them up for using a 3' extension cord to feed a wall clock.
That fire marshal had better not come into my house. :D
 

4x4dually

Senior Member
Location
Stillwater, OK
Occupation
Electrical Engineer/ Ex-Electrician
Personally, I use a good, quality, fencing staple. They have the strength to hold up really heavy gauge cordage and with the barbs, are assured to hold for the lifetime of the structure....but only if you drive them into the joists. LMAO

Screenshot 2022-02-17 071428.jpg
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
What code article prohibits this 2011 nec.
Presuming little changes in art 400 since 2011, try looking at 400.12(1) and 400.12(4) or wherever uses not permitted would happen to be covered if it has changed since then.

The ones I mentioned say not permitted (1) as substitute for fixed wiring of a structure and (4) where attached to building surfaces in 2020 NEC, but I don't think there has been any significant changes to those sections since at least 1999 or maybe 2002.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
A garage door opener operates for 30 seconds. I see no problem using a 16 ga SJ cord. Even the lamps are LED's, so that, and a direct drive motor has no startup current. I'd even do 18ga lamp cord across the ceiling.
And that makes it suitable for temporary wiring uses. Attaching the cord to the building surfaces and/or use of it as fixed wiring is not compliant with 400.12.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
400.1 Scope. This article covers general requirements, applications,
and construction specifications for flexible cords and
flexible cables.
Isn't NM a "cable"? Isn't it "flexible"? So why can Nm be used in this application, but not a hard service cord that is 100% tougher than NM ever will be.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Isn't NM a "cable"? Isn't it "flexible"? So why can Nm be used in this application, but not a hard service cord that is 100% tougher than NM ever will be.
NM though has some flexibility to it isn't intentionally designed to be used where it is flexed while in use.

Outer sheath of NM is thermoplastic and lasts longer than most flexible cords that often are rubber or synthetic rubber based.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
That's sort of a good question. Many people here claim that anything plugged into an outlet like an extension cord, is utilization equipment and thus not part of the electrical installation, so not subject to the code.

Someplace the NEC prohibits attaching a line cord to any surface. Somebody mentioned power strips, that's your answer.

-Hal
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Someplace the NEC prohibits attaching a line cord to any surface. Somebody mentioned power strips, that's your answer.

-Hal
And remember that attaching the power strip to the wall using screws and the keyhole slots in the strip keeps it from becoming part of the permanent wiring.

Anybody still installing recessed clock receptacles these days?
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
I was in a house a good number of years ago that the previous HO used zip cord. Everywhere.. I insulation would crack as you touched it. I've seen SJ cord do the same. I would expect the low cost import cord will do the same because if the goal is to save $$ on this install, I suspect we won't be spending a lot of money on this 18 AWG extension cord.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
I was in a house a good number of years ago that the previous HO used zip cord. Everywhere.. I insulation would crack as you touched it. I've seen SJ cord do the same. I would expect the low cost import cord will do the same because if the goal is to save $$ on this install, I suspect we won't be spending a lot of money on this 18 AWG extension cord.
I've seen that with zip cord as well. I blame the brittleness more on the fact that it probably was overloaded at times than the fact it was zip cord.
This is an 18 ga conductor supplying general use receptacles on 15, 20 amp circuit, or even in old places maybe someone put in a 30 amp fuse.

But if you keep load to within it's rating it still maybe doesn't last as long as other approved methods for use as permanent wiring.
 