hmspe
- Temple, TX
- PE
One of the local jurisdictions is very dilligent about having branch circuit lengths long enough so that the available fault current at lighting contactors, time clocks, receptacles, etc., is appropriate for the SCCR of the device. I'm seeing three approaches to the calcs.
A hypothetical system would have RK fuses in the service and 20A branch circuit breakers. Let's assume that the calculated fault current at the service is 65,000A and at the panel is 40,000A, on a 65K/10K series rated system. The first calculation approach uses the 40,000A at the panel as the basis for calculating the branch circuit conductor length required to reduce the fault current. The second calculation approach uses the "let through" of the the RK fuse (around 5000A) as the basis of calculation. The third approach adds a 20A fuse (usually class RK) just ahead of the control device and uses the let-through of that fuse to protect the downstream device, ignoring the fuse(s) and breaker(s) upstream.
I'd appreciate any thoughts on which method(s) are acceptable, and why.
Martin
Martin