Andpie
- 7 Reservior Rd
- E.E.
Can an electrical fault in a residence be transferred out onto the service grid affecting other homes in the area on the same secondary side of the transformer?
If you mean one transformer serving multiple houses, yes as Larry said it could blow the fused cutout serving the transformer. If it is a CSP transformer, it has a secondary circuit breaker and that would likely trip leaving your fellow neighbors in the dark. It is highly unlikely anything ahead of that single transformer would be affected.Can an electrical fault in a residence be transferred out onto the service grid affecting other homes in the area on the same secondary side of the transformer?
Or if a fault occured in customer owned service conductors on the line side of the service OCPD. Probably the most likely scenario for it, actually.Welcome to the forum.
Presuming the premises OCPD failed to open, yes, it could theoretically cause a primary fuse to open.
That scenario could affect those on other transformers as well.Low current faults to earth could cause elevated neutral to earth voltages for everyone connected to the same transformer.
For example a fault to a non bonded well case could inject current into the soil without tripping a breaker or fuse. But everyone on the same transformer would experience the soil voltage gradient caused by this fault.
Jon
VD issues, but actual damage would be stretching it, IMO.Ok well thank you everyone for that information. This is a great platform. When I said a “fault “ that was a very broad term. So that could cover just about everything.
So we know that the 220v / 240 v whatever the case may be is derived from the pole mounted transformer and we are not talking about a fault there. So correct me if I’m wrong but the voltage from the residence can never be more than it was supplied. That means we are talking about a fault current . In order to trip the network protection device on the primary side of the transformer the current would have to be extremely high. Agreed?
The service into the house looks unscathed. Main CB not tripped. Fire on the opposite side of the house from the service drop. So that means the fault was within a branch circuit. I’ll give you the benefit of doubt and say the fault occurred at an electric range on a 220v 50A CB. Question is - is that fault current enough to cause an issue at the neighbors house in anyway?
.. Question is - is that fault current enough to cause an issue at the neighbors house in anyway?
While that can happen, it is more often that the service conductors between the utility and the building act as fuses.Welcome to the forum.
I find that hard to believe that their fuses are set that high. I tripped out a CSP transformer once.While that can happen, it is more often that the service conductors between the utility and the building act as fuses.
And maybe suggest going after the POCO. They're the ones who brought the problem in.Just tell them "nice try".
Yes, sometimes the primary fuse blows, but typically they are sized not to protect the transformer, but to keep the next upstream fuse from opening. They want to keep the meters spinning as long as possibleI find that hard to believe that their fuses are set that high. I tripped out a CSP transformer once.
Cooper recommends about 4 times nameplate FLC for primary fusing. I don't know if that holds for what utilities typically use in practice or not.Yes, sometimes the primary fuse blows, but typically they are sized not to protect the transformer, but to keep the next upstream fuse from opening. They want to keep the meters spinning as long as possible![]()
I have seen utilities only carry two sizes of fuses on their trucks. These fuses are for their conductors of which they also carry a limited number of sizes.Yes, sometimes the primary fuse blows, but typically they are sized not to protect the transformer, but to keep the next upstream fuse from opening. They want to keep the meters spinning as long as possible![]()