growler said:
...I have seen voltage drops as high as 12-14% when #14 was used. People just don't think about how long many of the runs really are by the time they get to that last device. It really suprised me.
I'm willing to bet that most of those that use the argument of an unknown load have never measured nor calculated voltage drop for that last receptacle.
I think your 12 amps is a good size load to use for an estimate and that's what I use to check for voltage drop. ( I cheat and use the Sure Test to measure voltage drop)
Wow commercially we use 180VA as a projected load of general use receptacles; maybe you are using larger items in your home bedrooms then commercial sites? :grin:
Distances can go much farther than you may think when a circuit is actually installed. I've just unrolled some old plans of a 4,100 sq ft house that has a livable space footprint of 80'L x 40'W. It's a full custom home and there will be a sub panel 1/3rd of the distance from edge in a utility room. I can measure lineal footage (as it would get wired) from this sub panel to the farthest point, and accommodate for rise and fall, through devices and I have 170 feet to the last farthest outlet.
VD = 2.9% with 3.3A (396VA) load @ 170' from source, then
The next circuit closer has a distance of 150' to the last outlet
VD = 2.9% with 3.8A (456VA) load @ 150' from source, then
VD = 3.0% with 4.1A (492VA) load @ 140' from source, then
VD = 3.0% with 4.4A (528VA) load @ 130' from source, then
VD = 2.9% with 4.7A (564VA) load @ 120' from source, then
VD = 2.9% with 5.6A (672VA) load @ 100' from source, then
VD = 2.9% with 7.0A (840VA) load @ 80' from source
Voltage drop certainly does take place in all cases but there is a difference between voltage drop and damaging voltage drop. It occurs more with the increase of current/distance/the downsizing of conductors. 3% (3.6V) it's the most acceptable because it is referred to in the NEC.
If there are concerns with load there are safe way's to work with this like, sub panel (usually needed for circuit space anyway), smaller multi-receptacle circuit just for vacuum cleaner (halls, first outlet each bedroom)
Try a real test by plugging in a 12A vacuum in a 15A branch circuit turn it on and check voltage, try this in multiple locations, you can go father distances than you may think walking through a house. Make your results your policy it's you prerogative, but DON'T slander your pears to the public by scaring them to believe any less than #12 is dangerous!
Article 220 & example D2 reveal a way to safely calculate a residence:
Sub total other load
1st 10 KVA @ 100%
Remainder @ 40%
Total other load
Loads @ 100%
Largest motor @ 25%
Total VA
Unlike non-dwelling that must calculate continuous loads (lighting) @ 100% separate from non-continuous like receptacles (1st 10 KVA @ 100% & remainder @ 50%)
Article 220 & example D2 exemplifies the reality that only some items will be loaded some times by the fact the first 10 KVA is 100% and the remainder at only 40%. That is what a general lighting branch circuit is going through.
I'm one of those that use the argument of an unknown load :roll: