TWO IDEAS IN THIS THREAD, LOL.
1.- GARAGE RECEPS
I see it that if you plunk a receptacle under the panel on its own 20Amp circuit, you have met the garage requirement and are free to wire the door and 20 more receptacles on #14 if you so chose.
If panel is in the garage, yes.
Might want to see how your AHJ interprets this. I recently had a similar issue with inspector, but was over whether or not an outlet should have been on the "laundry circuit". Receptacle outlet was in same room as laundry equipment but not on same circuit. I told him I already have my "laundry circuit" and could put as many other receptacle outlets as I wanted in the same room and didn't matter if they had other outlets in other spaces on with them or not (except obvious prohibited like SABC circuits). He didn't see it that way and wanted all receptacle outlets in same room on the "laundry circuit". He eventually got his way, but I didn't give in easily. I still disagree that is what code says.