Some history becuse cut and pasting is easy. I will keep it too dwelling units.
2002 NEC
2005 NEC there were changes ....
2008 NEC Notice the loss of many exceptions.
2011 NEC
2002 NEC
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel.
(A) Dwelling Units. All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
(1) through (8) shall have ground-fault circuit-interrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas,
and areas of similar use
Exception No. 1: Receptacles that are not readily accessible.
Exception No. 2: A single receptacle or a duplex receptacle
for two appliances located within dedicated space for
each appliance that, in normal use, is not easily moved
from one place to another and that is cord-and-plug connected
in accordance with 400.7(A)(6), (A)(7), or (A)(8).
Receptacles installed under the exceptions to
210.8(A)(2) shall not be considered as meeting the requirements
of 210.52(G).
(3) Outdoors
Exception: Receptacles that are not readily accessible and
are supplied by a dedicated branch circuit for electric
snow-melting or deicing equipment shall be permitted to be
installed in accordance with the applicable provisions of
Article 426.
(4) Crawl spaces ? at or below grade level
(5) Unfinished basements ? for purposes of this section,
unfinished basements are defined as portions or areas of
the basement not intended as habitable rooms and limited
to storage areas, work areas, and the like
Exception No. 1: Receptacles that are not readily accessible.
Exception No. 2: A single receptacle or a duplex receptacle
for two appliances located within dedicated space for
each appliance that, in normal use, is not easily moved
from one place to another and that is cord-and-plug connected
in accordance with 400.7(A)(6), (A)(7), or (A)(8).
Exception No. 3: A receptacle supplying only a permanently
installed fire alarm or burglar alarm system shall
not be required to have ground-fault circuit-interrupter
protection.
Receptacles installed under the exceptions to
210.8(A)(5) shall not be considered as meeting the requirements
of 210.52(G).
(6) Kitchens ? where the receptacles are installed to serve
the countertop surfaces
(7) Wet bar sinks ? where the receptacles are installed to
serve the countertop surfaces and are located within 1.8
m (6 ft) of the outside edge of the wet bar sink.
(8) Boathouses
2005 NEC there were changes ....
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel.
(A) Dwelling Units. All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
(1) through (8) shall have ground-fault circuit-interrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas,
and areas of similar use
Exception No. 1 to (2): Receptacles that are not readily
accessible.
Exception No. 2 to (2): A single receptacle or a duplex receptacle
for two appliances located within dedicated space for
each appliance that, in normal use, is not easily moved from
one place to another and that is cord-and-plug connected in
accordance with 400.7(A)(6), (A)(7), or (A)(8).
Receptacles installed under the exceptions to 210.8(A)(2)
shall not be considered as meeting the requirements of
210.52(G)
(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a dedicated branch circuit for
electric snow-melting or deicing equipment shall be permitted
to be installed in accordance with 426.28.
(4) Crawl spaces ? at or below grade level
(5) Unfinished basements ? for purposes of this section,
unfinished basements are defined as portions or areas of the
basement not intended as habitable rooms and limited to
storage areas, work areas, and the like
Exception No. 1 to (5): Receptacles that are not readily
accessible.
Exception No. 2 to (5): A single receptacle or a duplex receptacle
for two appliances located within dedicated space for
each appliance that, in normal use, is not easily moved from
one place to another and that is cord-and-plug connected in
accordance with 400.7(A)(6), (A)(7), or (A)(8).
Exception No. 3 to (5): A receptacle supplying only a permanently
installed fire alarm or burglar alarm system shall not
be required to have ground-fault circuit-interrupter protection.
Receptacles installed under the exceptions to 210.8(A)(5)
shall not be considered as meeting the requirements of
210.52(G).
(6) Kitchens ? where the receptacles are installed to serve
the countertop surfaces
(7) Laundry, utility, and wet bar sinks ? where the receptacles
are installed within 1.8 m (6 ft) of the outside
edge of the sink
(8) Boathouses
2008 NEC Notice the loss of many exceptions.
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel.
(A) Dwelling Units. All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
(1) through (8) shall have ground-fault circuit-interrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas,
and areas of similar use
(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a dedicated branch circuit for
electric snow-melting or deicing equipment shall be permitted
to be installed in accordance with 426.28.
(4) Crawl spaces ? at or below grade level
(5) Unfinished basements ? for purposes of this section,
unfinished basements are defined as portions or areas of
the basement not intended as habitable rooms and limited
to storage areas, work areas, and the like
Exception to (5): A receptacle supplying only a permanently
installed fire alarm or burglar alarm system shall
not be required to have ground-fault circuit-interrupter
protection.
Receptacles installed under the exception to
210.8(A)(5) shall not be considered as meeting the
requirements of 210.52(G).
(6) Kitchens ? where the receptacles are installed to serve
the countertop surfaces
(7) Laundry, utility, and wet bar sinks ? where the receptacles
are installed within 1.8 m (6 ft) of the outside
edge of the sink
(8) Boathouses
2011 NEC
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel. Ground-fault circuit-interruption for personnel
shall be provided as required in 210.8(A) through (C). The
ground-fault circuit-interrupter shall be installed in a
readily accessible location.
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-
ampere receptacles installed in the locations specified in
210.8(A)(1) through (8) shall have ground-fault circuitinterrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor
located at or below grade level not intended as habitable
rooms and limited to storage areas, work areas,
and areas of similar use
(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a branch circuit dedicated to
electric snow-melting, deicing, or pipeline and vessel heating
equipment shall be permitted to be installed in accordance
with 426.28 or 427.22, as applicable.
(4) Crawl spaces ? at or below grade level
(5) Unfinished basements ? for purposes of this section,
unfinished basements are defined as portions or areas of
the basement not intended as habitable rooms and limited
to storage areas, work areas, and the like
Exception to (5): A receptacle supplying only a permanently
installed fire alarm or burglar alarm system shall
not be required to have ground-fault circuit-interrupter
protection.
Receptacles installed under the exception to
210.8(A)(5) shall not be considered as meeting the
requirements of 210.52(G).
(6) Kitchens? where the receptacles are installed to serve
the countertop surfaces
(7) Sinks ? located in areas other than kitchens where
receptacles are installed within 1.8 m (6 ft) of the outside
edge of the sink
(8) Boathouses