You can find out more than you want to know about bonding CSST here:
CodeNotes: Bonding of corrugated stainless steel tubing gas piping systems - ICC
Lee Clifton, senior director of PMG Resources for the International Code Council, discusses the bonding of CSST gas piping systems in this latest CodeNotes.www.iccsafe.org
Thank you. Answers two Questions I had: 1. The bonding system cannot be separate for the gas line. 2. The bonding system must connect to
the electrical grounding electrode in a meaningful, effective way.
The American Water Works Association wants grounding taken off water pipes and one (among other reasons) is that workers have been shocked
and hurt by electricity running through the water pipes. My question if you make a gas pipe an effective ground fault path does this not make a potential for disaster, you are not dealing with water, but gas?