jumper
- 3 Hr 2 Min from Winged Horses
NEC 220.52 says you use 1500VA for EACH small appliance branch circuit installed. You have to install 2 for the kitchen and one for the laundry. You can choose to install more and to me it seems like they would be counted at 1500 VA each.
Nope IMO. As long as I install at least 2, I seem to be covered.
(A) Small-Appliance Circuit Load. In each dwelling unit,
the load shall be calculated at 1500 volt-amperes for each
2-wire small-appliance branch circuit as covered by
210.11(C)(1).
210.11(C)(1) only says I gotta have 2, the rest are extra only.
NEC 220.54 says a dryer circuit is counted at 5000VA or the dryer nameplate, whichever is more. With no planned dryer, each one will have to be counted at 5 KVA.
Nope IMO no dryer is served in OP.
220.54 Electric Clothes Dryers ? Dwelling Unit(s). The
load for household electric clothes dryers in a dwelling
unit(s) shall be either 5000 watts (volt-amperes) or the
nameplate rating, whichever is larger, for each dryer
served.
For a range, this one is tougher. You have NEC table 220.55, and one could argue that you've never seen a range under 8 3/4 KW which would land you in column C. The smallest demand for a range in column C is 8 KW. I think if you did not install a range receptacle and just put a blank cover there, you could argue that no specific circuit was provided so no calculated value need be used.
The load for this is only the igniter, I will give you about 1A. let's see column A of that table says 80%. Wait it is old stove with a pilot light instead, 80% of 0 is.......