chris kennedy
Senior Member
- Location
- Miami Fla.
- Occupation
- Retired electrician
If this was your house would you want a fault current of 22k or a lightning strike directed to your gas service? I've been gray on this for years. Always been a AHJ call.
Gastite's tech bulletin might suggest you do that, but the NEC doesn't. In fact, what Gastite suggests is that the bonding point be as close to the servcie panel as possible, and close to the gas meter as also desireable.raptor22us said:THE NEC tells me to run a #4 bonding wire across the 70 feet of the house to the attachment for the gastite to the meter.

1793 said:I'm still at a quandary as to how to determine the conductor size.
mvannevel said:As I see it, the bonding of the CSST only becomes a Code issue in terms of following the labeling and manufacturers instructions.
90.2 Scope
(A)Covered. This Code covers the installation of electrical conductors, equipment, and raceways; signaling and communications conductors, equipment, and raceways; and optical fiber cables and raceways for the following:
yanici said:I sent an e-mail to the MA electrical board inquiring about the Gastite bonding situation. The response from Richard Fredette at the board was that we are to "comply with NEC 250.104(B)."
So, if I have two or three different electrical components that could energize a gas pipe, cook-top, range and fire place, I need to bond at each?cpal said:250.104 (B) is not cut and dry when considering the CSST manufactures requirments. 250.104 (B) has language that allows the EGC of the circuit which may energize the pipe to ast as the required bond.
(in part the sizing of the jumper) The bonding jumper(s) shall be sized in accordance with 250.122 using the rating of the circuit that may energize the piping system(s).
(also) The equipment grounding conductor for the circuit that may energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.
1793 said:So, if I have two or three different electrical components that could energize a gas pipe, cook-top, range and fire place, I need to bond at each?
cpal said:I knew this was going to open a can of worms.
I think the normal cord whip (or BC connection) when plugged into (or connected to) a receptacle with an EGC connection will satisfy 250.104 (B)
1793 said:As I mentioned in an earlier post, does anyone see a problem bonding from the water main to the first CSST fitting?
1793 said:From my conversation with the Inspector, lightning strikes are blowing the thin walls of this stuff.
1793 said:I would think if I went from the panel then this could act like part of the grounding system. Yes / No
1793 said:From my conversation with the Inspector, lightning strikes are blowing the thin walls of this stuff.
electricmanscott said:Is bonding with a "full size" conductor actually going to stop this?