e1793 said:In my opinion, NO. I think the inspectors point was nothing needs to be done at all. The requirement for the full sized bonding jumper was from the Technical Bulletin from WardFlex.
bottom line is if the listing instructions from the mfg requires a bond connection (250.66 type). Then it is going to be mandated, but untill there is a NEC or local requirement the responsibility is on the gas fitters. The theory should be that a permit is pulled and a licensed electrician installs the bond and the electrical inspector checks the installation.
But the current language in 250.104 (B) by itself does not require the installation that is required by the pipe manufacture.