Does the code require the GEC to be connected to the neutral bar or can it be connected to the ground terminal bar if a main bonding jumper is installed between the 2 bars
I would think it would depend on the bonding jumper size. I would reference art. 250.68 and 250. 64 and it does not say it must be connected to the neutral bar.
 

jwjrw

Senior Member
As long as you use a big enough bonding jumper and the connection isnt dependent on the "can" it should be ok
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The way we read 250.24(A)(1) we require it to be connected to the neutral bar directly.
(1) General. The grounding electrode conductor connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.
 
The way we read 250.24(A)(1) we require it to be connected to the neutral bar directly.
(1) General. The grounding electrode conductor connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.

I also read this section but if the panel has a bus tie between terminal bars would that change anything
 

jwjrw

Senior Member
I also read this section but if the panel has a bus tie between terminal bars would that change anything

Thats how I view it.I actually was allowed to do this by the most by the book inspector we have here. Not saying its code but seems to meet the intent.
 

jwjrw

Senior Member
The way we read 250.24(A)(1) we require it to be connected to the neutral bar directly.
(1) General. The grounding electrode conductor connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.

If you take the wording of that you could only connect to the bar the grounded conductor is hooked to right? Thats how I read it.
I swear I saw in ec@m a drawing that showed a jumper and saying its legal because the connection wasnt dependent on the can.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I have to agree with Gus here (I have to, because he agreed with me once recently, so I owe him one. :grin:)
I also read this section but if the panel has a bus tie between terminal bars would that change anything
It would not change the way electrons behave, as the two points are electrically connected. But it is not what the code words say to do.


Let's consider an absurd example. Suppose from the main service panel a feeder is run to a distribution board in the same room. Suppose that feeder has a "big enough" EGC. Can you connect the GEC to the ground bus in the distribution panel, since that bus is electrically connected to the ground bus in the main panel, which in turn is electrically connected to the neutral bus in the main panel, so it is essentially the same point, right?
 

jwjrw

Senior Member
I think it was around the code changes 08 issue. I think.
Im also looking for the one with a flood light switch in a bedroom.
Has anyone seen it? Arc fault related but swore he said it didnt need it not on bedroom circuit, not sure driving me crazy I cant find it.:D
 
I have to agree with Gus here (I have to, because he agreed with me once recently, so I owe him one. :grin:)It would not change the way electrons behave, as the two points are electrically connected. But it is not what the code words say to do.

Let's consider an absurd example. Suppose from the main service panel a feeder is run to a distribution board in the same room. Suppose that feeder has a "big enough" EGC. Can you connect the GEC to the ground bus in the distribution panel, since that bus is electrically connected to the ground bus in the main panel, which in turn is electrically connected to the neutral bus in the main panel, so it is essentially the same point, right?

Would that wire between the neutral in the main and the dist panel be a MBJ?
I think your example is a bit of a stretch

IMHO I dont know:)
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Would that wire between the neutral in the main and the dist panel be a MBJ?
I was speaking of two wires: the MBJ between the N and G bars in the main panel, and an EGC from the G bar in the main panel to the G bar in the downstream panel. As I said, it was an example of absurdity.

 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
So the other way to look at it is--- a mb panel with 2 factory neutral bars- one on each side of the panel. The grounded conductor is connected to the bar on the left side (remember this is also factory connected to the bar on the right side). Now are you all saying I cannot connect the GEC to the right bar? I don't buy it.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
as always a word game. 250.24(A) says the bus (singular).. at what point does the "bus" that the neutral connects to quit being "the bus". If the connection to the other bar is a wire then I'd think it was unacceptable. If its a factory strap/bar/whatever then it might be acceptable.
If one looks at the reasoning, as I understand it, the GEC wants to be connect to the neutral with as few of connections point as possible so as to carry the maximum current if called upon to do so,
For that reason, I would think we would want the connection as close as possible.
As with most things discussed here, Code compliance would be an AHJ call but it would, IMHO, certainly be good to encourage the connection to be as close as possible to the neutral connection to the bus. In most panels, it would be just as easy to connect there.
 

RUWired

Senior Member
Location
Pa.
250.24(A)4 allows the GEC to be connected to the equipment ground bar if there is a "wire or bus bar". If the bonding jumper is a screw then it is not allowed.

Rick
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So the other way to look at it is--- a mb panel with 2 factory neutral bars- one on each side of the panel. The grounded conductor is connected to the bar on the left side (remember this is also factory connected to the bar on the right side). Now are you all saying I cannot connect the GEC to the right bar? I don't buy it.


I don't either. If someone connected all of the circuit neutrals on the right side the factory jumper bar between the two would carry all of the neutral current. Seems like although the two are factory connected there essentially one neutral bar.
 