Bob, My memory fails me. Is it possible to open a General Duty switch with the handle in the "On" position, and not do so on Heavy Duty.
I've not tested that theory, but from opening a lot of switches, that may be the case.
Still leads, IMHO, to some interpretive reading for 110.17 but I can see the concern.
You da man Gus![]()
So they wouldn't object to a general duty safety switch with a padlock on it?
I suspect they wanted a horsepower rated switch (440.12) which, by definition, a general-use switch does not have; it has an ampere rating.
I'll have to have a look tomorrow, unless someone can post the text of that article, and save me the wait.![]()
110.27 Guarding of Live Parts.
(A) Live Parts Guarded Against Accidental Contact.
Except as elsewhere required or permitted by this Code,
live parts of electrical equipment operating at 50 volts or
more shall be guarded against accidental contact by
approved enclosures or by any of the following means:
(1) By location in a room, vault, or similar enclosure that
is accessible only to qualified persons.
(2) By suitable permanent, substantial partitions or screens
arranged so that only qualified persons have access to
the space within reach of the live parts. Any openings
in such partitions or screens shall be sized and located
so that persons are not likely to come into accidental
contact with the live parts or to bring conducting
objects into contact with them.
(3) By location on a suitable balcony, gallery, or platform
elevated and arranged so as to exclude unqualified
persons.
(4) By elevation of2.5 m (8 ft) or more above the floor or
other working surface.
:grin:
No I am not trying to set anyone up here, this one perplexed me in the class. They put out an easy question and being the cocky SOB I am I spoke right up and said yes only to be told I was wrong.
They gave me a code section, it is not 110.3(B) but I don't want to give it up yet. I am really interested to find out if anyone else feels the same as the instructors did. I know I was not convinced even though they clearly felt strongly that they where on solid ground. ....... Don't they know who I am? :grin:
Anyway, their argument was that since the terminals aren't guarded then the homeowner can get shocked trying to replace a fuse...blah blah blah. I can see their point
I can see the concern, what I do not see is any code to back it up.
.
Can we use a general duty safety switch as the disconnecting means for a HVAC unit located outside a dwelling unit?
That is all you need. Might I presume that I would be correct in believing that in a "General Duty Safety Switch," the live parts are inside an enclosure? I will go on as if I had received the answer "yes.". . . live parts . . . shall be guarded against accidental contact by approved enclosures or . . . .