So Bob - this was a 'class' - did you learn anything? As if this is an example of the class - I'm not to impressed by the siting of 110.27A... :roll: If so there should also be a lock on any enclosure with the keys kept by the AHJ to issue to qualified persons in the event access is required.
14KV HAVC gear at a residence...I know all the Ac disconnects never get a lock on them, well most of them, but reading 110.31(D) would seem to require it, and I'm surprised they didn't cite this code to back up their claim, but then again if a lock was installed it would be code compliant in both citations.
what I do not see is any code to back it up.
14KV HAVC gear at a residence...
...........I have argued that because there are no live parts accessible, then it shouldn't require the working space as in 110.26, as there are no live parts likely to be worked on while energized, but that went no where.:roll:
Assuming the wacky citation even pertains to disconnects, the difference between General Duty and Heavy Duty has nothing to do with cover interlocks. Cover interlocks are brand specific.
Siemens 3R general duty disconnects over 60A all have cover interlocks. Can I mount one of those outside my house according to your instructor?
The way I read NEMA KS1, all disconnect switches have cover interlocks. The only difference is that a HD switch is allowed to have a screw that defeats the interlock.
I hope that they are not inspectors. :roll:
Well...actually.......:roll:
Shouldn't one of those jumpers be black? :grin:I don't see a problem. It sure beats the disconnect shown below.
No, they specifically cited 110.27(A) and the fact a GD switch can be opened in the on position.