Is it any wonder why myths persist in the trade? :roll:
This is the root of the problem with misinformed Inspectors, they are being taught wrong in the begining.
Is it any wonder why myths persist in the trade? :roll:
There must be more than one standard as many discconects have no interlock at all ........ or maybe that is a new standard?
Read (past, not present, tenseI don't agree with the instructors, but I think their problem was that the hypothetical switch was located outside and not in one of the protected locations mentioned in items (1) through (4) of 110.27(A).
...
Thanks for the citation, Bob. Now here is my answer to your instructors:
That is all you need. Might I presume ...
Count me in for a bigon the 110.27(A) citation. Seems as though I've installed more than a couple AC Disconnects without any guarding over the terminals to speak of, but I wouldn't swear to it. ...![]()
Read (past, not present, tense) carefully, items (1) through (4) are alternates to the basic 110.27(A) rule which is "... live parts of electrical equipment operating at 50 volts or more shall be guarded against accidental contact by approved enclosures ..."
Sad thing that it's only a wrong answer on an exam but it would be a violation in the field and a re-inspection.