hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
From a resent thread of a problem of OCPD's opening when a generator transition from one source to another, it was stated the cause was motors being "out of phase" or acting like generators "out of phase" with the source?
While I know I have studied this over the years much has been forgotten as much time has passed by since my days at school.
First I have always thought that only single phase generators have the problem of being out of phase (180?) which would double the available voltage of the fault the transition would load into when the ATS switched into it, another words two 240 volt sources transitioned into each other at 180? crossing would effectively put 480 volts into the fault causing the available fault current to be very high.
But the issue I'm not fully understanding I guess is when we have 3-phase source transition back into another 3-phase source we are only looking at rotation and sync, and the most you can be out is 60? which is dead between 120? phase shift of a normal Polly phase system, the transition is not looking at whether source 1 pole A is lined up with source 2 pole A because in a Polly phase system it doesn't care as long as the two sources have the same rotation, in a single phase system it would be a problem because of the fact they would be 180? out.
First we don't have to involve discussion of when we transition two prime mover sources as we can clearly see that the mass of the prime mover is so much more to sync that the two sources would take much longer to line poles up (get into sync) and high current would last much longer resulting in OCPD's opening or failure of one source or the other so this would be another subject.
But with motors I find it harder to understand the problem as first the rotation will or should be the same from one source to the other if nothing has changed, second at the point of 60? being in the middle, meaning 60.9999? the motor would speed up to catch up with sync or at 59.9999? the motor would slow down to sync , while this would produce a surge it should not be at full lock rotor current, from what I figure around 50% of LRA and since the breakers would be designed to handle the full LRA they should not be opening in this situation if sized properly.
So I guess what I'm not understanding is if this problem is more like the problem with transformers where the left over residual circulating current in the transformer windings can cause an out of phase event when we transition from a generator back to the utility too fast, kind of an inrush type problem with an added kick, do motors also have this problem?
so if possible can we discuss this problem to maybe get my mind to wrap around this problem to better understand it?
I guess maybe it is because I haven't experience this type of problem before as I have with transformers so I have never really thought about it until it came up in the other thread?
While I know I have studied this over the years much has been forgotten as much time has passed by since my days at school.
First I have always thought that only single phase generators have the problem of being out of phase (180?) which would double the available voltage of the fault the transition would load into when the ATS switched into it, another words two 240 volt sources transitioned into each other at 180? crossing would effectively put 480 volts into the fault causing the available fault current to be very high.
But the issue I'm not fully understanding I guess is when we have 3-phase source transition back into another 3-phase source we are only looking at rotation and sync, and the most you can be out is 60? which is dead between 120? phase shift of a normal Polly phase system, the transition is not looking at whether source 1 pole A is lined up with source 2 pole A because in a Polly phase system it doesn't care as long as the two sources have the same rotation, in a single phase system it would be a problem because of the fact they would be 180? out.
First we don't have to involve discussion of when we transition two prime mover sources as we can clearly see that the mass of the prime mover is so much more to sync that the two sources would take much longer to line poles up (get into sync) and high current would last much longer resulting in OCPD's opening or failure of one source or the other so this would be another subject.
But with motors I find it harder to understand the problem as first the rotation will or should be the same from one source to the other if nothing has changed, second at the point of 60? being in the middle, meaning 60.9999? the motor would speed up to catch up with sync or at 59.9999? the motor would slow down to sync , while this would produce a surge it should not be at full lock rotor current, from what I figure around 50% of LRA and since the breakers would be designed to handle the full LRA they should not be opening in this situation if sized properly.
So I guess what I'm not understanding is if this problem is more like the problem with transformers where the left over residual circulating current in the transformer windings can cause an out of phase event when we transition from a generator back to the utility too fast, kind of an inrush type problem with an added kick, do motors also have this problem?
so if possible can we discuss this problem to maybe get my mind to wrap around this problem to better understand it?
I guess maybe it is because I haven't experience this type of problem before as I have with transformers so I have never really thought about it until it came up in the other thread?