I would think that if you install the double throw switch ahead of the existing service disconnect then you would be required to separate the neutrals and grounds in the existing service per 250.24(A)(5) and relocate your grounding electrodes to the dt switch.
what he said (if the loads to be served are greater than 100A then no, unless you can engineer some load shedding in there somewhere)
The user of the optional standby system shall be permitted to select the load connected to the system.
...as in replace the service disconnect with a service-entrance-rated manual transfer switch?...the manual transfer switch either has to be service rated or have a disconnect with OCPD's ahead of it to the service, if the service already has a outside disconnect and you put the MTS between it and the panel, your good to go.
Hmmm.... I don't understand unless you put in a FUSED double throw switch.I would think that if you install the double throw switch ahead of the existing service disconnect then you would be required to separate the neutrals and grounds in the existing service per 250.24(A)(5) and relocate your grounding electrodes to the dt switch.
Hmmm.... I don't understand unless you put in a FUSED double throw switch.
.
Must it be fusible ???
250.24 states: (5) Load-Side Grounding Connections. A grounded conductor shall not be connected to normally non?current-carrying metal parts of equipment, to equipment grounding conductor(s), or be reconnected to ground on the load side of the service disconnecting means except as otherwise permitted in this article.
(emphasis added)
Is a service rated non-fuses DT switch a service disconnecting means ?[/COLOR]
I would think we might get various opinions on this.
I would say a non-fused DT switch is the service disconnecting means
provided you comply with section 230.91
I'm getting a foggy picture of your comment.At this point, what does "located immediately adjacent thereto" mean?
To me, it means it is part of or nippled to the enclosure with the overcurrent device. So, in a residential application (actually, any application where the persons are not properly trained), if there is a length of cable from the non-fused disconnect to the transfer switch, and then from the transfer switch to the original service, I would not accept it as an inspector - based on my experience and the wording I see in the above supplied section number. JMHO
As noted by others, ocp must be integral or located imediately adjacent thereto to qualify as a service disconnecting means. If you put a service-equipment-rated, non-fusible DT switch ahead of the existing service disconnecting means, nothing changes as far as the service disconnecting means. The DT switch enclosure, conduits, etc. would get bonded to the grounded conductor, or in the case of an ungrounded system would require an equipment bonding jumper.Must it be fusible ???
250.24 states: (5) Load-Side Grounding Connections. A grounded conductor shall not be connected to normally non–current-carrying metal parts of equipment, to equipment grounding conductor(s), or be reconnected to ground on the load side of the service disconnecting means except as otherwise permitted in this article.
(emphasis added)
Is a service rated non-fuses DT switch a service disconnecting means ?
I would think we might get various opinions on this.
what he said (if the loads to be served are greater than 100A then no, unless you can engineer some load shedding in there somewhere)
I need to know wareto find in the code ware you must change over to flex from emt thanks