Zog, did not have a chance to get into trans. area today. I did get the info of the module on mainbreaker. all the numbers are in a box and "in " outside box.
1. long delay setting = 1.0 ln
2.long delay time = 7 sec @ 6 ln
3.short delay pickup= 3 ln
4. short delay time = .5 sec
5. gfi pickup = b ln
6. breaker trips 6t & gft test amps 3ln
7. gf time .5 sec
All the building feeds had one of the settings set at 24 , I think it was the long delay . Thanks again
With your six 500kVA transformers feeding a single 4000A breaker, assuming Z=5% for your transformers you have about 72,170A of available fault current comming into that gear.
Your arc flash currents will be somewhere above 27,424A and less than the 72kA.
Your breaker does not have an INST trip function, so you will have a time delay in an arc flash event that will cause Ei to be way higher than if you had Ei.
There is no way, based on the info you have posted, that this equipment is within the limits of the tables and your facility is required per the NFPA 70E to do an arc flash analysis.
Now there is a simple solution, you can retrofit your breaker you described above with an arc flash reduction switch, like the Quick Trip system from Utility Relay. Basically what it does is allow you to flip a switch and have "maintenence setting" on you trip unit, we do several of these every day and have seen most results reduce arc flash HRC's from 4 or dangerous, to 1 or 2 with the switch on.