ivsenroute
- Florida
Can you have the meter pulled?:grin:
The $1,000 per day fine for every day of non-compliance under State Law is more effective.:grin:
What article did you site here? I can't find it.
"Cite"
The spelling police are everywhere!!!
If we have to price a job without visiting the location, is it "sight unseen" or "site unseen?" :grin:
PLEASE tell me you told him:The $1,000 per day fine for every day of non-compliance under State Law is more effective.:grin:He then told me to call him when I know what I am talking about.
His response was:
* What was left on the SE cable was the equivalent to a #4.
This comes from a 200A OH service and this disco goes to the main panel subfeed.
Point him in the direction of table 250.66 and explain that #4 would be just great if it were copper but the minimum size GEC for 4/0 Al SEC cable on a 200 amp service is #2 al.
Hi ivsenroute, in your post #17 you mentioned the guy failed to remove paint from the enclosure prior to installing the lug. I was thinking if that would be necessary in such an enclosure, if one were to look in any panel it appears as though the factory installed ground bars are mounted right onto the enclosure's surface with no effort made to remove the coating. Even when one bonds the isolated neutral bar in a main panel situation it's only the screw's threads making contact with the enclosure and the head of the screw making contact with the bar. So my question would be does the paint still need to be removed in such a situation?