What EGC? From the beginning of this in the other thread, we were presuming no grounded surfaces present in an electrically isolated tub. Throwing in a grounded object for the potential victim to contact or for current to pass to via the water changes all the parameters of the experiment, and if you do have such current flowing outside the GFCI protected conductors that is more then the trip threshold - you will trip the GFCI whether there is a EGC present or not at the GFCI location. Unless you have water with no impurities chances are with a 120 volt source the water is conductive enough to carry the necessary 4-6 mA necessary to trip the GFCI.
I believe that FZ is separately asserting that if a working EGC is connected to the appliance in question and that EGC is connected to metal, even if only a terminal on the end of the cord, anywhere in the appliance where water can get at it, then current will flow to the EGC and the GFCI will trip.
Whereas if there is no EGC present (as simulated by his two wire experiment) there cannot be any current imbalance and so the GFCI will not trip.
The question of how much current will actually flow on a path through the water outside the appliance body, this will depend strongly on the geometry and the stated experiment will test only one set of conditions. Note that in the experimental setup one of the meter electrodes was closer to one of the conductor wires than the other wire was. This is definitely a worst case compared to a user at some distance from the appliance.
The way the meter was used, it gives us a very rough approximation of how much current would flow (compared to the total current) if a zero resistance person were bridging between the same two points in the water. Putting a foil on the end of each electrode and putting a 3K resistor in series with one meter lead would give a much better approximation.