i have an customer requesting his apartments receptacles be replaced. does these need to be afci at breaker or receptacle?
what about bathroom kitchen, do i need to install afci and gfci in kitchen being kitchen is required to be afci. any thoughts?
(4) Arc-Fault Circuit-Interrupter Protection. Where a
receptacle outlet is supplied by a branch circuit that requires
arc-fault circuit-interrupter protection as specified
elsewhere in this Code, a replacement receptacle at this
outlet shall be one of the following:
(1) A listed outlet branch-circuit type arc-fault circuitinterrupter
receptacle
(2) A receptacle protected by a listed outlet branch-circuit
type arc-fault circuit-interrupter type receptacle
(3) A receptacle protected by a listed combination type
arc-fault circuit-interrupter type circuit breaker
This requirement becomes effective January 1, 2014.
(3) Ground-Fault Circuit Interrupters. Ground-fault
circuit-interrupter protected receptacles shall be provided
where replacements are made at receptacle outlets that are
required to be so protected elsewhere in this Code.
Exception: Where replacement of the receptacle type is
impracticable, such as where the outlet box size will not
permit the installation of the GFCI receptacle, the receptacle
shall be permitted to be replaced with a new receptacle
of the existing type, where GFCI protection is provided
and the receptacle is marked “GFCI protected” and
“no equipment ground,” in accordance with 406.4(D)(2)
(a), (b), or (c).
I think that 406.4(D)(4) is clear on afci
It is also clear for Gfci in 406.4(D)(3)
Just curious Dennis:
You have a receptacle in a 1960's vintage home, and it needs to be replaced. You believe the code requires the replacement receptacle to be an arc fault or the breaker feeding it needs to be arc fault? Could not the "where required" be intrepreted as "where required at the date of constrcution"?
Man, as if I don't have enough problems with arc fault breakers in new homes, this opens up a whole new can of worms.:happysad:
You can interpret it that way but I think the authority having jurisdiction may laugh at you. It would make no sense to make that a requirement as you stated
Does it make a lot of sense to allow you to replace a panel and not require Arc Fault breakers and then require them if you change out one receptacle?
No as some interpet that you need to add AFCI under the 2011 code, I interpet that way.
Even if Arc Faults receptacles were to work just how much good would it do to replace only one ?
The added cost is just going to keep people from replaceing old receptacles that really need to be replaced or get a handyman to do it.
Dennis I know you didn't write the code but it doesn't make a lot of sense as written if safety were the motivation.
I agree with the others that the GFCI protection of the replacement, where specified in the current Code that applies in your customer's jurisdiction, is required, and there is no way to avoid it.i have an customer requesting his apartments receptacles be replaced. does these need to be afci at breaker or receptacle?
However, AFCI is another matter. If you pigtail the new replacement receptacles onto the existing wiring with just a little bit of new conductor, this pigtail allows you to invoke 210.12(B) Exception and waive the AFCI. This works under the 2014 NEC only, and is so solid (though heretical to some of the safety minded) that the removal of it applying to 406.4(D) Replacements is having to be added to the 2017 NEC.
Similar conversation here, which I had at a residential final just this Tuesday. Inspector shared the experience he had of inspecting another contractor's panel, where a branch circuit conductor, connected to a brand new AFCI breaker, was continuously arcing and never tripping as they stood and watched and waited. . . .I've had conversations with inspectors about how useless AFCI is, right on the job site where he encouraged me not to put them in.
There is no 210.12(B) Exception in the 2011 NEC.Al so how do we deal with code 406.4(D)(4) in the 2011 code . . . ?
Al so how do we deal with code 406.4(D)(4) in the 2011 code where is states:
outlet shall be one of the following: ..............
What is being changed in the 2017 ?
Well, you see, my comment to the OP, above was limited to the 2014 NEC and speaks to the 210.12(B) Exception. And when you asked me about what you do about the 2011, I tried to point you to the fact that I said my comment was limited to the 2014 NEC.and I was not talking about that exception to the code. that does not appear to 2014.
What I have read of the 2017 NEC NFPA reports of what is developing, looking at 210.12 specifically, has had new added text to 210.12 that limits the 210.12(B) Exception to NOT be used on 406.4(D).
What will be in the final result of the 2017 NEC is still not known, at least by me.
Well, I guess I'm going to be lawyer bait:
1) I don't have to pull a permit to repair existing wiring in a home
2) I wouldn't pull one anyway to replace a receptacle(s)
3) No one will know I didn't pull a permit or install arc fault protection unless I'm ratted out by the owner (very unlikely) or I cause a fire by my replacing the receptacle (which I would hope the probability of which is rather low).:happyno:
I would think that in most States a contractors license says you shall work as per code regardless if inspected.