Good catch 210.19.
Good catch 210.19.
Because a NEMA-14 has become the commonplace receptacle for these things when they are cord-and-plug connected. I think that's because the NEMA-14/50 is what you find in full hook-up RV parks, so they can bring their charger with them and recharge at an RV park.Just curious, watched a couple charger install videos and am wondering why people are using Romex 6/3 when the chargers only need 2 hots and a ground, I was planning to use 6 gauge 6/2 with a #12 ground On a 60 amp breaker . One guy terminated the white wire in the panel and put a wire nut on the wire in the charger unit, not a lot of spare room to start with. Why are people using 6/3 with the extra unused neutral? I’ve never hooked one up, am I missing something, maybe for future use for a different charger that needs 120/240?
some charger mfg actually recommend against gfci as it sometimes will conflict with the charger and create nuisance tripping. Direct wire eliminates this issue, and the charger is required to be gf protected on IT'S outlet anyway.
Can you order some 6-2 mc it's not as expensive as it could be and may be easier for you vs trying to pull in conductors into flex.After sleeping on this I came up with a new plan. Cut the sheet rock channel in a 3/4 metallic flex, pull in 2 #6’s and a #10 ground, (THHN) install a 60amp regular breaker. Then spend the rest of the weekend repairing sheet rock and painting. It’s more work but it will look perfect when done and most of all code compliant. #6 THHN @ 75degree is rated for 65amps. Plus with a raceway if the charger requirements change there’s some flexibility to add a neutral. 3/4” flex up to (4) #6’s
To put a little background on this, some EVSEs use sophisticated ground connection validation. A typical scheme involves putting intermittent pulses of current through the ground to check the characteristics, e.g. resistance and impedance. While these pulses are below the nominal trip current, the sharp edges or specific pattern can look like high current leakage, triggering an upstream GFCI to trip.
If it came from the line side it might if it's a pulse of 6ma then there'd be 6ma missing from the CT on the nuetral and other hot.No type of pulse on an EGC should cause a GFCI to trip.
Can you order some 6-2 mc it's not as expensive as it could be and may be easier for you vs trying to pull in conductors into flex.
Minnestoa is now on 2023. Or was the permit opened before 2023 adoption?This would be installed in the next couple weeks so it would be under the 2020 NEC. I did reach out to another electrician in Minnesota and he said he's put 5 in recently and the inspector did not require GFCI protection, I just wanted to double check.
I think Zoro has the Bryant for like $50.If you install a $20 14-50R, chances are you’ll be back within a year to replace it after it melts.
A Hubbel or Bryant quality receptacle is close to $100.
My friend later clarified he was referring to the direct connection so he was fine without the GFCI breakerMinnestoa is now on 2023. Or was the permit opened before 2023 adoption?
If you install a $20 14-50R, chances are you’ll be back within a year to replace it after it melts.
I believe they are only tested to carry 40 amps continuously.Crazy question but how in Hades are these cheaper 14/50 even for sale if they are such a fire hazard? I assume they are Labeled/Listed.
No doubt a 48A continuous load would melt a 50A receptacle and I suspect that is what all those posts on social media are about.I have no doubt that with the steady 48amp draw for 6-8 hours and a loose connection this will heat up and cause damage.