I don't believe this. Show the evidence that AFCI breakers do anything to prevent fires.
What has been proven that AFCIs can not stop a glowing arc and that there is no way an arc can be sustained at 120V. AFCIs are useless other than the ground fault component
GFCIs are different, and anyone who understands the difference between the two technologies would not compare them.
I am not comparing the function of an AFCI to a GFCI despite the fact that I encounter licensed electricians on a daily basis that do not understand how either device functions. The statement was made to reflect that when people do not understand the technology, they routinely scoff at it.
There is a plethora of data that reflects that AFCI has resulted in property damage reduction as well as a reduction to human injuries and death as a result of electrical fire. You can look this up for yourself if you don't accept what I posted. How do you think these requirements become code? They are approved by code making panels with data presented to reflect their necessity. Many codes are the result of a previous documented incident. The insurance industry has a significant influence in the making of codes. Code panels don't just arbitrarily accept proposals without data to batten the request.
ActionDave
Chief Moderator
Durango, CO, 10 h 20 min from the winged horses.
Licensed Electrician
....There is a plethora of data that reflects that AFCI has resulted in property damage reduction as well as a reduction to human injuries and death as a result of electrical fire.
There is none. The only data that exist about AFCIs is how they fail to perform as intended.
What you posted was a list of stats about fires in general. If there was any evidence that AFCIs were effective I would be in favor of them.
It's a sad and sorry tale. The short story is they were rammed into the code by the manufacturers.
Many are, that's how code changes and additions should work.
If AFCIs were effective insurance companies would be offering financial incentives to policy holders to have them installed.
That is both false and naive. We have rules about automatic transfer switches and generators that were rammed into the code by generator manufacturers with no evidence of problems.
We have rules about derating wires on roof tops that were rammed into the code by the copper producers with no evidence of prior failures.
The three story limit on the use of romex was removed as a horse trade between code panel members to get a favorable vote on another proposal.
In use receptacle covers, changing the listing on rain tite fittings, ....and on it goes
PaulMmn
Union, KY, USA
EIT - Engineer in Training, Lafayette College
...In use receptacle covers...
Well, the screw-on caps (with the beaded chain so they don't get lost), the flip-up caps, and IIRC the 'front door' style of protection for outdoor outlets all have issues.
When you plug in the Christmas lights for their 4-month display, I'm glad there are the bubble covers to keep the connections dry.
Biggest problem with in-use covers is the ones that don't have gaskets around the cord exits, and don't give a clear view of the interior. I do NOT like wasps!
peter d
New England
This is why I say manufacturers should have no direct participation in the code making process. I'm fine with them serving in an advisory role but I'm adamantly opposed to them being directly involved in the code making and voting process.
hbiss
EC, Westchester, New York NEC: 2014
Hawthorne, New York NEC: 2014
EC
I'll say it again- the code making panels have representitives who work for the manufacturers and are voting members. This is where all that manipulated data you found came from. We've seen it all before. They used it to help convince the other members to vote with them.
We ain't just a bunch of hicks here. Some of our members sit on code making panels themselves so we know what goes on.
One of our members (and a manufacturer's rep) who I believe was a voting member of the CMP that was involved with AFCIs, was so pompus that he was banned from here for a few months. Basically he told us to go screw ourselves if we don't agree with AFCIs. We need to do what they tell us to do and it isn't going to change. Nice.
Remember one thing, there's a lot of money being made off this if you know what I mean.
-Hal
That's a statement without proof. There is data regarding the effectiveness of AFCI vs. 1950's technology circuit breakers.
What I posted were the latest stats about fires in general when compared to previous stats reveals a substantial decrease in electrical fires which cause property damage, injuries and death. I'm certain there are other factors but if there are so many that disagree with the effectiveness of AFCI, work towards changing the code.
I can't argue with that but why is it that residential sprinkler systems haven't been added to the code? They've been proposing that requirement for 20 years.
I'm glad that we agree on something here, however: you stated that manufacturers can force things into the code so apparently that's not always how it works. I refer again to the sprinklers.
Why would an insurance company offer a discount for something that is required by code already? Insurance companies routinely compel property owners to change fuse panels and Federal Pacific panels or threaten to cancel the policy. I have no love for insurance companies myself.
I'm not certain about what in particular you are claiming to be false and untrue but research 702.12B and follow the protracted path that requirement leads you down. The requirements are poorly written and they should just come out and say that electronic circuitry is required to ensure that "all ungrounded conductors can be simultaneously disconnected," "disconnects shall be capable of being locked in the open position," "shall be capable of being locked with or without a lock applied." Electrical inspectors are backed into a corner with these requirements. The state once again replies that these installations require a variance. There are numerous codes that are improperly written, difficult to comprehend or explain to the electrician or just plain wrong. As an inspector, we don't ge tto pick and choose which codes we like.
Copper producers? More likely electrical engineers.
I don't have knowledge of that however; where's the proof that there was ever a reason to limit the installation of NM cable to three stories?
I don't disagree. Time to retire rather than fight a corrupt system on a daily basis.
hbiss
EC
Think about it. AFCI's haven't been installed in a large enough base yet to cause such a "drastic" change in data. And of the ones installed we know that they don't work. So, yeah, there are other factors at work here.
We already talked about changing the code and the only way that's going to happen is litigation. There is just too much money at stake here for any one party to just throw in the towel.
nysprkdude said:
... why is it that residential sprinkler systems haven't been added to the code? They've been proposing that requirement for 20 years.
And we've been saying the same thing for 20 years! We are all big proponents of sprinklers. All I can surmise is that it's a different code and sprinkler manufacturers don't have the deep pockets the the electrical industry does to lobby for the changes.
There are plenty of dwellings that are between fuses and brand new that could be retrofitted with AFCI breakers.
nysprkdude said:
... where's the proof that there was ever a reason to limit the installation of NM cable to three stories?
Same reason that it can't be used in places of assembly for instance. NM is not a "robust" wiring method. Where there are large numbers of people in one place you don't want to rely on an electrical system that can be compromised by an over-driven staple or rodents.
jap
Yet it's perfectly acceptable to be used in a dwelling unit where we eat, sleep, and spend 3/4's of our time. :)
JAP>
romex jockey
Vermont
electrician
These don't trip as much>>>
~RJ~
tortuga
Code Historian
Oregon
Electrical Design
The question you all seem to be debating is should UL standards drive the NEC
or should the NEC drive the UL and other construction & performance of equipment standards?
The NEC used to cover the construction & performance, installation and mintenence of electrical equipment.
The future scope of the NEC is basically restricted to installation of electrical equipment in new construction and retrofits.
When the NEC requires Equipment to be Listed it generally is assuming UL’s Standards Technical Panels (STPs) provide the construction & performance requirements for the electrical equipment.
In reality an AHJ can adpot any IEC or other listing standard or waive the requirement for listing (as is necessary with raintight EMT fittings used with Bell boxes).
Since around '02 there has been a push to remove product construction & performance requirements from the NEC.
I suspect the NEC is a little more 'open' of a standard than the UL or other construction & performance standards a AHJ should adopt.
And removing construction & performance standards from the NEC may have been a mistake.
kwired
Electron manager
NE Nebraska
The first required AFCI's are just starting to get old enough that we may start to see if they are any good at preventing fires. Then comes the question of whether they still function at their age. The biggest concern for electrical fires in the permanent wiring of a structure IMO is the "glowing connection" though, which AFCI's will not detect.
Seems to me the manufacturers are driving both UL and NEC more than anybody else is.